I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the difference between a verilog task and a verilog function?
if ELCB and RCCB connected in series,what wiil be the result
why phase always came one direction in 5pin socket(right hand or left hand) which direction and why..........?
Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.
Is 3C x 2.5 Sqmm Cable can withstand 40Amp Starting current? If Yes then specify your ans.
i heard that power factor(PF) is the main concern for industries, if they are maintaining PF around 0.6 they will be fined for that. now the question is, how can they improve the PF ranging between 0.9 to 0.95 which is safe for them i,e escaping from the fine?
What technology is used in latest generators?
what happens if generator is running leading power facotor?
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
xlpe cable 4 core nuetral wire is small why ?
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
why current transformer secondary is short circuited an what will happen if connect very high resistance acrossthe secondary side of current transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)