I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the use of 6.6kV/6.6kV Transformer???
Why Indian Electricity frequency desined 50 Cycles as developed countrys are using high frequency with low voltage
what is the meaning of DY-11 Z-5%
Why the motor take high starting current for long time(10- 15 sec) which is connected to Blower as compaire with a motor which is connected with pump with same rating?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
why dc motor runs slowly when dc supply is given?
WHAT IS THE SHOPE TESTING
what is the method of earthing of a transformer using electrodes?
what is the principle of servo motor
define the active power?
What is the use of Gateway RTU like ABB RTU 560 in power plant, SAS system ?
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)