I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
| Is This Answer Correct ? | 2 Yes | 0 No |
what is different between kvar & micro farad when its comes across the capacitor rating is it possible to convert kvar to mf or mf to kvar
is there any chance to get shock from the transformer oil at the time of maintenance due to its dielectric property. . ?
What is the normal value of delta in rotor angle stability or transient stability? Why it selected so?
I am abt to give IOCL intrv.Plz sir guide me for IOCL intrvw (Electrical).Which subject to be consider. questions are generally asked from which subject.Plz help me out.
why transformer calling in VA rating
If the generator will trip, what you will do as an electrical technician in charge.
what is the difference between direct loading and indirect loading?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
how does it help for selection of a transformer.
How to check VFD outgoing voltage
A 100 KW GENERATOR , only 50 kw load is connected then how much power generated by generator
How are harmonics produced in AC machines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)