IF we have 500kva transformer 11.0/0.415V, 50Hz. How to
calculate the current on HT & LT side, how can we consider
for its breaker (HT & LT both)? You are requested to solve
the question herewith.
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
current on HV side= 500/(1.732*11)
= 26.24 A
current on LV side= 500/(1.732*0.415)
= 695.6 A
Breaker on HV side will be 630 A VCB (since it is the
lowest available VCB and in HV side you have to go for
VCB/SF6)
Breaker on LV side will be =greater than (1.2*695.6)A i.e.
834.72 A
so we consider it to be 1000 A ACB
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / a.i.a
As, usually the ultimate load current for any distribution system take 20% spare loads for future , so full load current shall be multiplied by 0.2 more (i.e 1.2) to calculated MCCB rating.
hope you got the correct answer.
Is This Answer Correct ? | 0 Yes | 0 No |
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
What is the function of mid point voltage in battery bank
1 Answers Jindal Steel and Power,
why are transformers rated in KVA and not in KW
What is the deference between earth fault & earth leakage
what are the steps involved in generator load test?
in single phase converter, the no.of scr's conducting during overlap a)1 b)2 c)3 d)4
What is vacuum circuit breaker.define with cause and where be use it device?
Buchholz relay is used ………. a) protection T/F b) oil T/F c) Air core T/F
8 Answers Engineers India Limited,
Can we pass 11kv power in 1.1kV voltage grade cable.If not why?.
How can you measure the signal from the PT100 sensor?
how many testing is necessary for 27 MVA transformer?
can we connect transformer with star conected secondary to delta connected primary in series?