IF we have 500kva transformer 11.0/0.415V, 50Hz. How to
calculate the current on HT & LT side, how can we consider
for its breaker (HT & LT both)? You are requested to solve
the question herewith.
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
current on HV side= 500/(1.732*11)
= 26.24 A
current on LV side= 500/(1.732*0.415)
= 695.6 A
Breaker on HV side will be 630 A VCB (since it is the
lowest available VCB and in HV side you have to go for
VCB/SF6)
Breaker on LV side will be =greater than (1.2*695.6)A i.e.
834.72 A
so we consider it to be 1000 A ACB
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / a.i.a
As, usually the ultimate load current for any distribution system take 20% spare loads for future , so full load current shall be multiplied by 0.2 more (i.e 1.2) to calculated MCCB rating.
hope you got the correct answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
ful form of gis
what is form factor.and rms value..
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
What shall be minimum thickness of firewall in between two transformers and which code specifies it ?
what is the current rating of 2500 KVA,33KV/433v transformer on secondary(LT) side
9 Answers Reddy Labs, Vitrum Glass,
what will happen if dc machine are supplied by ac source??
Why sometime i receive GCU fault /Excitation voltage loss in my Generator Synch Panel .
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
What will happen if 40W and 60W Bulb is Connected in Series.
what will happen if the input of a transformer is dc?
How could i check the earth connection of my home using a multimeter?????? If it is possible plz help me....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)