Answer / ramniveth

i agrre with this answer with little correction
Standby Earth Fault relay is also connected to star side

the difference between SEF and REF is REF operates in
InZone only
SEF operates in In and Out Zones. If there is an earth
fault in outgoing feeders and the feeder protection is not
operated then SEF operates .
Tripping time for SEF will be more than REF and Earth fault
protection in O/G feeders.

Is This Answer Correct ?    112 Yes 11 No

what is the diff. b/w restricted earth fault relay & standby earthfault relay and where they a..

Answer / oes

Restricted earth fault (REF) relay is a unit protection
intended for one winding of a transformer (neutral winding)
the input of which is from a neutral bushing CT and in some
applications, balanced by the output of three line CTs in
the Y-winding directly connected to neutral. This provides
accurate sensing of zero-sequence leakage currents for a
fault within its zone of protection, i.e., on the windings.
Whereas, standby EF relay is a back-up overcurrent ground
protection usually connected on the HV side and its main
purpose is to provide local back-up protection in case for
a failure of main protections of the LV feeder/line prots.,
bus prots., and the transf. main protections.

Is This Answer Correct ?    78 Yes 28 No

what is the diff. b/w restricted earth fault relay & standby earthfault relay and where they a..

Answer / shirish prajapati

The REF and SBEF are two separate protection functions. The
REF will protect the transformer winding and the cables to
the breaker. SBEF is standby earth fault protection. It is
backup protection in case of uncleared faults out on the
network, or earth faults outside the REF zone. It may also
protect the neutral earthing resistor if there is one, and
may act as a cheap busbar protection system by tripping the
LV bus section first and the transformer LV C/B second. Do
you really want to compromise important backup protection
for the cost of a neutral CT? You have the option to get
another CT fitted in the bushing, or if there is a neutral
cable terminated on the bushing you could install a slipover
CT on the cable, or in the NER cable box. Lots of
possibilities, and not very expensive.

Is This Answer Correct ?    31 Yes 8 No

what is the diff. b/w restricted earth fault relay & standby earthfault relay and where they a..

Answer / hari

REF is a kind of protection that is connected to the Star Wnding CT which has a neutral connection.It covers only the protection of restricted regions like windings,breakers & cables.

Wherein SBEF relays are connected to the Star Windings and it detects the Zero sequence current in the neutral CT's.

Is This Answer Correct ?    1 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

transmisancy eficencey calculation formula

1 Answers  


what voltage generated earth tester meter when we testing the Earth point ?

1 Answers   Cognizant, CTS,


why electrical power has benn needed for speed controller of woodward governor control for biomas power plant

1 Answers  


define transformer

1 Answers  


What is the importance of creepage distance in disc insulator ?

1 Answers  






from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?

1 Answers  


AT THE TIME OF INSTALLING THE POWER PLANT POWER IS TAKEN FROM NEARBY GRID AND GIVING THE SUPPLY TO THE GENERATOR WHICH ACTS AS MOTOR. WHAT IS THE NEED OF RUNNING THE GENERATOR AS MOTOR?

6 Answers  


Can anyone explain how the vector diagram of a transformer which doesn't have name plate be found whether it is Dy11/Dy5/Yd11 and so on?

4 Answers   TATA,


I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?

0 Answers  


CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?

22 Answers   L&T,


what is the effect of power factor of machines in starting current

0 Answers  


what are adantages of OC and SC test over the load test?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)