i agrre with this answer with little correction
Standby Earth Fault relay is also connected to star side
the difference between SEF and REF is REF operates in
InZone only
SEF operates in In and Out Zones. If there is an earth
fault in outgoing feeders and the feeder protection is not
operated then SEF operates .
Tripping time for SEF will be more than REF and Earth fault
protection in O/G feeders.
Is This Answer Correct ? | 112 Yes | 11 No |
Answer / oes
Restricted earth fault (REF) relay is a unit protection
intended for one winding of a transformer (neutral winding)
the input of which is from a neutral bushing CT and in some
applications, balanced by the output of three line CTs in
the Y-winding directly connected to neutral. This provides
accurate sensing of zero-sequence leakage currents for a
fault within its zone of protection, i.e., on the windings.
Whereas, standby EF relay is a back-up overcurrent ground
protection usually connected on the HV side and its main
purpose is to provide local back-up protection in case for
a failure of main protections of the LV feeder/line prots.,
bus prots., and the transf. main protections.
Is This Answer Correct ? | 78 Yes | 28 No |
The REF and SBEF are two separate protection functions. The
REF will protect the transformer winding and the cables to
the breaker. SBEF is standby earth fault protection. It is
backup protection in case of uncleared faults out on the
network, or earth faults outside the REF zone. It may also
protect the neutral earthing resistor if there is one, and
may act as a cheap busbar protection system by tripping the
LV bus section first and the transformer LV C/B second. Do
you really want to compromise important backup protection
for the cost of a neutral CT? You have the option to get
another CT fitted in the bushing, or if there is a neutral
cable terminated on the bushing you could install a slipover
CT on the cable, or in the NER cable box. Lots of
possibilities, and not very expensive.
Is This Answer Correct ? | 31 Yes | 8 No |
Answer / hari
REF is a kind of protection that is connected to the Star Wnding CT which has a neutral connection.It covers only the protection of restricted regions like windings,breakers & cables.
Wherein SBEF relays are connected to the Star Windings and it detects the Zero sequence current in the neutral CT's.
Is This Answer Correct ? | 1 Yes | 15 No |
motor and transformer working with same principle so why motor rotor was roted and transformer not roted
Why double earthing is required ?
URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA TRANSFORMER 11KV/415 VOLTS, AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH INDUCTIVE LOADS, LIGHTING LOADS,ETC., HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW TO CALCULATE.
Pls explan the OLR setting in VCB at HT yard
Based on CPI/CGPA they shortlist the candidates & than directly start Interview so there is no Written Exam or GD Only PI.Interview held @ MNNIT , ALLAHABAD On-Campus on 6th,Aug, 2007 & the Questions asked to me by Interview Board ( 4 People) are from HR/SummerTraining/BTP/Subject-core, POWER SYSTEM & MACHINE. time duration of I/V is about 15-20 Minutes. HR- Q.1 Name,hobbies & About family background ? Q2.What u know abt NTPC ?? Q3.Why u want to choose NTPC as ur Carrier's starting i.e power sector not any other Oragnisation or sector ?? Techincal Questions- Q1.What is the reason for transformer Noise ?? Q2.Which material is used for making Transformer oil & How u measure its dielectric strength & Name the test ? Q.3 Which Machine u will prefer 2 use if flammble gases are coming out at a place & why ?? Q4.What is relation b/w Transmission Lines & Communication Lines ? Q5.What is the maximum capacity Synchronus Machine & total powerGeneration in our country ? Q.6 In india Power generation is at 50Hz while in America its 60 hz ,why so ?? Advantage or disadvantage ?? Q.7 Maximum Generation Voltage in india ? Q8. What is the Voltage regulation & why its required n how much is permissible ? & causes of voltage variation ?? Q.9 Why electric shock is feel ?? n in a Electric Train why we didnt feel that ? Q.10 Have u seen/ experience of any power plant/ industry related to the power sector ? so these are the questions which not too diffcult i think was asked to me.
which is more dangerous AC\DC supply
WHaT IS THE CONCEPT OF INDUCTION LAMPS IN MODERN LIGHTINGS, and HOW IT WORKS TO EMIT LIGHT ( AS NO ELECTRODES ARE PRESENT ) ?" COULD INDUCTION LAMPS CAUSE INTERFERENCE WITH COMUNICATIONS INTO A STORE USING INDUCTION LIGHTING ? WHAT IS THE BENEFIT OF USING THE LOW FREQENCY INDUCTION LAMP , VERSUS LED , AND VERSUS FLUORESCENT, AND VERSUS ANOTHER KIND OF LIGHTING . THANK yOU MOISES GUINDI
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
what is the purpose of starter in tube light?what is it operation .
why transformer measures in kva
1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.
what is the difference between potential Transformers and capacitive voltage transfoemers and where it is used?