i agrre with this answer with little correction
Standby Earth Fault relay is also connected to star side
the difference between SEF and REF is REF operates in
InZone only
SEF operates in In and Out Zones. If there is an earth
fault in outgoing feeders and the feeder protection is not
operated then SEF operates .
Tripping time for SEF will be more than REF and Earth fault
protection in O/G feeders.
Is This Answer Correct ? | 112 Yes | 11 No |
Answer / oes
Restricted earth fault (REF) relay is a unit protection
intended for one winding of a transformer (neutral winding)
the input of which is from a neutral bushing CT and in some
applications, balanced by the output of three line CTs in
the Y-winding directly connected to neutral. This provides
accurate sensing of zero-sequence leakage currents for a
fault within its zone of protection, i.e., on the windings.
Whereas, standby EF relay is a back-up overcurrent ground
protection usually connected on the HV side and its main
purpose is to provide local back-up protection in case for
a failure of main protections of the LV feeder/line prots.,
bus prots., and the transf. main protections.
Is This Answer Correct ? | 78 Yes | 28 No |
The REF and SBEF are two separate protection functions. The
REF will protect the transformer winding and the cables to
the breaker. SBEF is standby earth fault protection. It is
backup protection in case of uncleared faults out on the
network, or earth faults outside the REF zone. It may also
protect the neutral earthing resistor if there is one, and
may act as a cheap busbar protection system by tripping the
LV bus section first and the transformer LV C/B second. Do
you really want to compromise important backup protection
for the cost of a neutral CT? You have the option to get
another CT fitted in the bushing, or if there is a neutral
cable terminated on the bushing you could install a slipover
CT on the cable, or in the NER cable box. Lots of
possibilities, and not very expensive.
Is This Answer Correct ? | 31 Yes | 8 No |
Answer / hari
REF is a kind of protection that is connected to the Star Wnding CT which has a neutral connection.It covers only the protection of restricted regions like windings,breakers & cables.
Wherein SBEF relays are connected to the Star Windings and it detects the Zero sequence current in the neutral CT's.
Is This Answer Correct ? | 1 Yes | 15 No |
Which factor decide the colour of the light emitted from a Led?
I have done my m.tech in electrical engg discipline. Can any one please suggest me how should I prepare for getting into phd in iit or nit.How should I prepare for getting into lecturership
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
WHAT IS DIFFERENCE BETWEEN idmt and instentanous relay? is idmt is used as back up protection or else?or when instantenous relay saturates IDMT will operate???
what is V=4.44FBN, THIS 4.44 ONLY U GOT the voltage in term sof 11, 22 etc this 4.44 u will get from form factor which has a value of 1.11
What are the advantages of a three-phase system over a single-phase system?
What is the full name of one of choke less lamp BLL
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
our plant maximum demand has 500 kva.need to suggest me to maintained pf 0.98.how much capacitor bank will be connect to the supply line.
Igfet is a
what happen if the supply is given to the stator of the 3phase induction motor with out assembling the rotor ?
what is trip circuit supervision relay? How does it work in switchgear?
6 Answers Radha Regent Hotels,