Answer / bilal hamad
1- to isolate supply and load in case of faults and power harmonics (to protect the source) and also to protect the load .
2-KWH: the real power (useful) consumption per hour.
KVAH: the total power consumption per hour.
KVA: the total power (real and imaginary)(vectors sum).
KVARH: the imaginary power consumption per hour.
in summary: the power factor will control the amount of real (active)power and reactive power. all real loads are usually inductive loads or resistive, this will reduce the power factor and then increase the reactive power, the solution is to install capacitor banks to increase the power factor and then reduce the reactive power so increase the active power.
3. CT: is a step down current transformer used for current measurement and protection.
PT or VT: is a step down voltage transformer used for voltage measurement.
| Is This Answer Correct ? | 9 Yes | 1 No |
What is the difference between Derived earth Fault and measured earth fault.How it works.
Off-circuit Tap changers in distribution transformer required
What is the black star?
what is the affect of earth's magnetic field on the frequency used in aircraft???
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
What is time response of the control system?
why mccb is not tripping when phase & neutral terminal are interched ?
State norton’s theorem?
What you have to see in transformer after week, month?
What is the significance of %Z in case of transformer?
Transmission voltage is kept 11KV,33KV,66KV,132KV,220KV due to form factor. What happen to 400KV and 765KV transmission voltage?
Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)