1.what is use of isolation transformer.
2.Differance between KWH,KVAH,KVARH,KVA.
3.Main use of the CT and PT.
Answer / bilal hamad
1- to isolate supply and load in case of faults and power harmonics (to protect the source) and also to protect the load .
2-KWH: the real power (useful) consumption per hour.
KVAH: the total power consumption per hour.
KVA: the total power (real and imaginary)(vectors sum).
KVARH: the imaginary power consumption per hour.
in summary: the power factor will control the amount of real (active)power and reactive power. all real loads are usually inductive loads or resistive, this will reduce the power factor and then increase the reactive power, the solution is to install capacitor banks to increase the power factor and then reduce the reactive power so increase the active power.
3. CT: is a step down current transformer used for current measurement and protection.
PT or VT: is a step down voltage transformer used for voltage measurement.
| Is This Answer Correct ? | 9 Yes | 1 No |
Diffrectiate between earthing and neutral
What is difference between slip rings and carbon burushes?
i want to estabilish an loss energy storage system,such that it can store electricity lost during the transmission of electricity in conductor,so that this system stores energy lost during transmission and supply it to street lights during night
Earth Is a very good conductor or very good insulator.? If a good conductor then why current donot flow through small piece f earth and if a good insulator then why we use it as return path in lines.???
srij i need the relationship b/w KW AND KWH and with an electrical example. plz send if u can?
I need a 33/690V Dry type transformer.How to select IP class for this transformer.This will be an outdoor transformer located in a highly polluted environment.
If a high resistance fault occurs,then what are the changes will happen in the system?
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
I have 3KVA Libert GTX2 UPS. I need to calculate the back up time with some load. How to calculate the Back time. I need the expert guide
Can i get some examples of mechanical devices?
HI FRIENDS,MYSELF & MY GROUP OF FINAL YEAR ELECT ENGG. ARE MAKING A 50/3HZ,5HP,1000RPM,440V SALIENT POLE SYNCHRONOUS GENERATOR.COULD ANYONE OF U TELL ME WHAT COULD BE THE ADV. & DISADVANTAGES OF MAKING SUCH A LOW FREQN.GENERATOR/
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)