URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA
TRANSFORMER 11KV/415 VOLTS,
AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH
INDUCTIVE LOADS, LIGHTING LOADS,ETC.,
HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH
RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH
RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW
TO CALCULATE.
Answer / sudhakar g
For any transformer it is better to install two for body
eathing and two for Neutal earthing
Body Earthing: GI pipe 40mm dia using charcoal and salt
like this
Neutral Earthing: Copper plate 600x600x3 mm size for
netural earthing with all neccesary materials
After completion of Earthing you need to check the earth
resistance value for these earthing it should be below 3ohms
I think these are the neccasary requiremnts for your
trasnformer
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
What is Bolted fault?
How test for Ddo vector group test condition?
Differentiate AC and Dc resistance
WHAT IS A COLOUR CODING OF 3 CORE CABLE
what is V=4.44FBN, THIS 4.44 ONLY U GOT the voltage in term sof 11, 22 etc this 4.44 u will get from form factor which has a value of 1.11
what is the formula to find Amp. for an 3 phase moter both if H.P. or if kW is known?
what ll happen to current if two phases get short circuited
a transformer runs by electro-induction principle like all motors.then why dosen't it rotate just like any other motor
what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?
why dc source used for HV breakers and Relays operation?
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)