If connected load of Asphalt plant is 375Kw. What suitable
KVA DG set is required. What is calculation formula. what
extra load have to consider. in what efficiency it will
work.
Answers were Sorted based on User's Feedback
connected load=375kw
kva=kw/cos phi
kva=375kw/.8
=468.75
extra load= 20% (assume) i.e 468*20%= 93.6
total 468.75+93.6=543.68 kva say 550kva
eff. 375/550*pf (0.8)*100=85%.
| Is This Answer Correct ? | 25 Yes | 2 No |
Answer / munish saini
KW=KVA*PF
PF=.8
KW=375
KVA=KW/PF,=375/.8=468.75KVA
20 Percent required more as eppiciency Factor
so required dg should be=562.5 KVA
| Is This Answer Correct ? | 4 Yes | 1 No |
Dear friends,
Total Connected Load = 375 KW
KVA required @0.8 PF = 375 /0.8 = 468
Taking a 0.8 as a Demand Factor = 468 *0.8=375 KVA
Considering running of D.G set on 80% load = 3750.8=468 KVA
Considering 20% load for future expansion = 468 + 20%(93KVA)
Total KVA of D.G set = 561 KVA
you can go with 600 KVA D.G set .
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / srinivas
if the connected load of plant is 375kw. but any time all
the load may not be there. if peak load may be 300kw at any
instant so KVA rating of DG=KW/cos(phi) so you can take
300/0.9= 333.33 so you can take 350KVA Dg you can go for.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / syed.yaseen
dear friends,
Given kw = 375
suitable kva = 375/.8 =468.75
Future extra load consider = 20% ie.. 93.75kva
total kva = 468.75 + 93.75 = 562.5
as per company designed capacity preferred is 625kva dg set
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / vikash gupta
calculation formula:-kva rating=kw rating/cos phi
connected load=375w
kva=kw/cos phi
kva=375w/.8
=468.75w (ans)
extra load=(468.75-375)w
=93.75watts(ans)
efficiency =375*100/468.75
=80%
| Is This Answer Correct ? | 6 Yes | 14 No |
Answer / sam
calculation formula is KVA= KW*Pf(cos phi)
KVA= 375*.9
KVA=337 so DG set will be more than 20% of rated KVA
| Is This Answer Correct ? | 21 Yes | 34 No |
what is the safety of voltage power transformer(2250KVA0
what is the calculation formula for motor starting torque,running torque, running torque.
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
What is frequency?
how we findout a ignater is faulty or not?
What is power factor?How to improve power factor
Why, the starting current of 3 phase Induction Motor is 7 to 8 times its rated current?
What id difference between power and energy?
Define norton equivalent circuit?
How can we save theft of wire after finishing of wiring work, plz suggest another answer other than security or supervisor's work?
single phase for 230 then why three phase are 440 volt
Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)