what type of relays used in transformers?
Answers were Sorted based on User's Feedback
Answer / latika
1] O/C Relay both Alarm + Trip
2] E/F Relay both Alarm + Trip
3] Differential Relay both Alarm + Trip
4] Bucholz Relay both Alarm + Trip
5] WTI cum Protection both Alarm + Trip
6] OTI cum Protection both Alarm + Trip
7] Oil Level Indicator with Alarm
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / pavan
over current relay
earth fault relay
buchholz relay
differential protection
under voltage protection
under frequency protection
under voltage protection
over voltage protection
low oil level
high temp protection relays
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jagdish sandhanshiv
In addition to these relays - there is new addition called -
Relay for tap changer control and transformer monitoring
System... for more info contact Jagdish 9867976570 -
jagdish@a-eberle.de
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / rajesh
There is relay which is in control room or else in outdoor
kiosk it can be fitted up relay is call microprocessor
based numerical RTCC
| Is This Answer Correct ? | 1 Yes | 10 No |
railway exam in asst loco pilot old test paper
25 Answers Indian Railways, Loco Pilot, RRB, Southern Railways, TATA, Vimal,
In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)
what is diff. b/w of earth & neutral?. why we are separately using ?
What is the difference b/w Earthing and Grounding?
sir, how to select the cable size, what is the parameters use ang what is the formulas use for this cable size calculations. please tell me.
Why choke coil is connected in series with starter in tubelight??why starter is connected in parallel to tubelight??
What is the diffrence between ofline ups and online ups?
why PD testing for power cables
1 Answers Bhushan Power Steel, CSE, Datre Corporation,
What will be cross section area of copper conductor for carry 2000 amps & 2500 amps....sq.mm.?/
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
Leakage current,un balance current which relay using for high voltage transmission?
block diagram of 2 ups system connected in hot stand by mode?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)