On what basis no of earth pits are to be decided either for
transformers or for equipment?
Answers were Sorted based on User's Feedback
Ans: Transformer secondaty sholud have neutal point. This
we brought from earth. neutral point is earthed and
connected to T/F. for this we required one earh pit. and
for body earthing we should have another earh pit.
structure earthing for this another earth pit.
For an equipment we required only one earth pit for body
earthing and electrical accessories earthing( like
motors,switch gear, electronic instruments).
Is This Answer Correct ? | 23 Yes | 13 No |
There should be two distinct earth pit for TR neutral and
one for body earthing. This is as per IER. The earth
conductor crossection will depend upon the max fault
current that could flow in the system in case of a fault.
The thumb rule is, the crossecton of the earth conductor
should at least be half of one phase conductor.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / farrukh
First of all we need to know ,Why we earth the transformer
neutral,? and the answer is that ,
Transformer has three out put phases and at any time all
these phases loads are not equal, so when the load is
unbalanced on any phase, the current may flow in neutral
line,and to dissolve the current at transformer end we need
to earth the neutral. Neutral pits are used to to provide
best conductive earth.
Is This Answer Correct ? | 10 Yes | 7 No |
Answer / kartik
No of Earthing pits for a equipment depends upon components
of equipments prone to flow of fault current during
abnormal condition.Say for transformer, metal body &
neutral may carry fault current.So 2 nos pits for
transformer is required.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / meka sekhar
normally, transformer body is conned to earth mat via earth
cables. No earth pit is required for body connection.
Normally Earth pit will be provided for neutral earthing
in order to facilitate isolation.
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / sathihsa
earth pits for tr depends on kva rating and fault current
use to carry.........
Is This Answer Correct ? | 9 Yes | 17 No |
Answer / shvetang
the no of earth pits are depends upon the amount of earth
fault current that occurs during working of any equiment
Is This Answer Correct ? | 1 Yes | 12 No |
What is the advantage of AC supply?
Why all voltage level are multiples of 11, like 220V, 440V, 1100V instead of 200V, 400V, 1000V?
9 Answers Indian School of Mines,
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
what is deffrence between squirral cage and wound rotor in IM?
How wti of transformer works?
On 400 amp factory load how kvarh capacitors provide
what is the different between second harmonics and third harmonics ?
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
How can w select the cable size for different rating load & also waht r factors affecting the during selection of cable?
11 Answers AB Inc, Bosch, BRB Cable, Lucas TVS, Trisome Technical Services,
how can we change the supply frequency?
what kvrah y we need to take the readind of that
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.