What is the min and max ohmic value for earthing?
Answers were Sorted based on User's Feedback
Answer / sham
it's depend on system
Basicaly for LV system it should be less than 1 ohm and
for MV system it should be in rage of 1 to 5 omh
ideal is 0 resistance but practically it is not possible
| Is This Answer Correct ? | 43 Yes | 1 No |
Answer / satya dev ( knight frank)
It is depending on usage
LV- for copmutor/ electronic device --- 0- 1 ohm
for UPS --- 0- 1 ohm
HV - for substaion/ power generating system- 0- 5 ohm
but 0 is not possible.
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / ahmed
It depends on the system and the resistivity of the
soil .Minimum is less than 1 ,Maximum is 10 ohms .
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / mgalalkhedr
For derty Earth: the min is zero as ideal case and the
maximum shoildn't more that 1.5 ohm.
For Clean earth the min as before and the maximum is 1 ohm.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / r prakash
The whole list of answers is confusing.
No one is telling the correct values for a normal
Industrial machinery which sometimes includes sophisticated
machinery using Computers and electronics circuit.
I want to check the earthing status of some of the Earths I
did about 5 years ago in my factory.
Can someone help me in this.
R Prakash
rprakash@rataneng.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / arjun
Individual value should be less than 5 Ohms , as low as
possible, Combined value to be < 1 ohms , it is not
dependent on voltage level
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ajay
Ideally zero
for generating substation 0-1 ohm
for transmission system 2-4 ohm
for distribution system 2-5 ohm
| Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between earhing and neutral
Why the vector group of excitation transformer in static excitation system is Dy5?
Why we use stones in switchyard?
What is the temperature and cooling aspects of dc motor
what is the meaning of transformer short circuit test?
How to find the length of a Xlpe cable required to transmit 3mva load at 22kv.
from which formula we select a capacitor rating?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
why star point of motor shall not be grounded?
what are the analog quality input for protection function?what are minimum reqiments?
Why is negative feedback invariably preferred in closed loop system?
why t/f are rated in kva. is it conserned with p.f.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)