Answer / sham
it's depend on system
Basicaly for LV system it should be less than 1 ohm and
for MV system it should be in rage of 1 to 5 omh
ideal is 0 resistance but practically it is not possible
| Is This Answer Correct ? | 43 Yes | 1 No |
Answer / satya dev ( knight frank)
It is depending on usage
LV- for copmutor/ electronic device --- 0- 1 ohm
for UPS --- 0- 1 ohm
HV - for substaion/ power generating system- 0- 5 ohm
but 0 is not possible.
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / ahmed
It depends on the system and the resistivity of the
soil .Minimum is less than 1 ,Maximum is 10 ohms .
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / mgalalkhedr
For derty Earth: the min is zero as ideal case and the
maximum shoildn't more that 1.5 ohm.
For Clean earth the min as before and the maximum is 1 ohm.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / r prakash
The whole list of answers is confusing.
No one is telling the correct values for a normal
Industrial machinery which sometimes includes sophisticated
machinery using Computers and electronics circuit.
I want to check the earthing status of some of the Earths I
did about 5 years ago in my factory.
Can someone help me in this.
R Prakash
rprakash@rataneng.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / arjun
Individual value should be less than 5 Ohms , as low as
possible, Combined value to be < 1 ohms , it is not
dependent on voltage level
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ajay
Ideally zero
for generating substation 0-1 ohm
for transmission system 2-4 ohm
for distribution system 2-5 ohm
| Is This Answer Correct ? | 0 Yes | 0 No |
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,
pls send previous bhel electrical papers
can we use existing delta star with neutral grounded,step down(6.6kV/415V), 3 phase power transformer bi-directionally.
How do we calculate the resistance per metre of single core aluminium stranded cable 19*3.25mm sheathed in pvc,at 15 deg C temperature?
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
i want use the cable size 16cx4 core aluminium usege watts 240x2000w this cable size is correct?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
what is the earth resistance
What is the inside of ACB & VCB & SF6 breaker's pls tell me about this
how to take the 3 phase ups input and collect single phase output
Ammeter of 1 ohm resistance measure max 10 ohm to measure higher resistance from it
if u want to buy a motor than what will be the configuration of that motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)