What is the min and max ohmic value for earthing?
Answers were Sorted based on User's Feedback
Answer / sham
it's depend on system
Basicaly for LV system it should be less than 1 ohm and
for MV system it should be in rage of 1 to 5 omh
ideal is 0 resistance but practically it is not possible
Is This Answer Correct ? | 43 Yes | 1 No |
Answer / satya dev ( knight frank)
It is depending on usage
LV- for copmutor/ electronic device --- 0- 1 ohm
for UPS --- 0- 1 ohm
HV - for substaion/ power generating system- 0- 5 ohm
but 0 is not possible.
Is This Answer Correct ? | 32 Yes | 4 No |
Answer / ahmed
It depends on the system and the resistivity of the
soil .Minimum is less than 1 ,Maximum is 10 ohms .
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / mgalalkhedr
For derty Earth: the min is zero as ideal case and the
maximum shoildn't more that 1.5 ohm.
For Clean earth the min as before and the maximum is 1 ohm.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / r prakash
The whole list of answers is confusing.
No one is telling the correct values for a normal
Industrial machinery which sometimes includes sophisticated
machinery using Computers and electronics circuit.
I want to check the earthing status of some of the Earths I
did about 5 years ago in my factory.
Can someone help me in this.
R Prakash
rprakash@rataneng.com
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / arjun
Individual value should be less than 5 Ohms , as low as
possible, Combined value to be < 1 ohms , it is not
dependent on voltage level
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ajay
Ideally zero
for generating substation 0-1 ohm
for transmission system 2-4 ohm
for distribution system 2-5 ohm
Is This Answer Correct ? | 0 Yes | 0 No |
In case of any eventuality, who is your next of kin?
2 Answers Edison, Foster Wheeler, GE, GE Energy, HP, Infosys, Koch Industries, Roper Industries, Siemens,
why the auxilary(starting)winding is provided in single phase inductoin motor?
how to calculate the earth mat design in 132 kv substation yard ????
0 Answers Divis Laboratories, KSEB, SWPL,
Can we connect two CT'S to one energymeter?
what is the earthing condition between earth & phase.
What is mean CT Saturation? How to calculate?
What is the LUX
why connecting surge unit in contactor coil
what is the difference between potential transformer and capacitive voltage transformer?
explain the application of reciprocity theorom
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
what is the significant for using two types of voltage(line voltage & phase voltage)