What is the formula for finding fault level of generator?
Answers were Sorted based on User's Feedback
Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
Is This Answer Correct ? | 0 Yes | 1 No |
Can anyone explain the power flow in flouresent lamps (tube lights) .What are the functions of Starter & choke used there?
What is the abbreviation of NGT panel
what is the difference between the diode and the rectifier
17 Answers Avalon, L&T, Mahacol Trexim,
how to get bearing & winding temperature of an induction motor?
What are the procedures followed for underground cable laying.....???
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
one split ac how can told of this ac which Tr tell me us
Why indian power system in 11kv,22kv,33kv,66kv,110kv,220kv ? 2) Why ups required dedicated earth?
could mail me the question papers for the test.
Is there any difference of regulation of transformer, alternator , transmission line, if yes, what is it?