What is the formula for finding fault level of generator?
Answers were Sorted based on User's Feedback
Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
| Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
| Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
| Is This Answer Correct ? | 0 Yes | 1 No |
there are 3 transformers each of 1500 kva and one transformer of 1000kva for a 11 floor building . total otgoing kw is 4066 kw. i need an extra 260 kw .is there any provision for that? what is the max kw that can be connected with these transformers?
Can step down transformer works as step up one???
What will happen if the voltage in my house drops from 220V to any lower voltage?
what is the meaning of the HT LT transformer?
what is the differnce b/w voltage and current
How to check AC & DC Choke
How single phase & 3 phase motor select rotating direction ie clockwise/anticlockwise
What is the value of 3 phase voltage?
what is the formula of knowing the clabe size on any load?
What are the causes of motor vibration?
why are you use the crgo core lamination in transformer
Brief working principle of fluorcent tubelight,function of starter & choke.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)