what is general test conduted by transformer
Answers were Sorted based on User's Feedback
Answer / rahul deo purohit
Short Circuit TEst And open circuit test
| Is This Answer Correct ? | 25 Yes | 3 No |
The General test conducted on transformer is
1.Insulation resistance test
2.Open circuit test
3.Short circuit test
4.Double voltage and double frequency test
5.High Voltage test
6.Resistance test
7.Vector group test
8.Magnetic balance test
9.Break Down Voltage test
| Is This Answer Correct ? | 19 Yes | 3 No |
open circuit and short circuit test.
impulse test.
Megger test.
| Is This Answer Correct ? | 18 Yes | 4 No |
Answer / arya anup
mainly open circuit,short circuit test in order tomeasure
core loss & copper loss. then megger test to check the
insulation level between lv & HV coils.next is high voltage
test to measure capability to withstand impuse of very high
voltages( about 28kV will be applied between HV & Earth)
Then coms double voltage and double frequency test,where
we apply double the rated voltage on to the lv side with
100Hz frequency. this helps to find out insulation problems
between phase to phase.(All tests should be done with oil
inside only)
Oil also to be checked for its break down voltage(shold
with stand minmum 30kV)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / raja
1.OPEN CIRCUIT TEST
2.SHORT CIRCUIT TEST
3.VECTOR GROUP TEST
4.MAGNETIC BALANCE TEST
5.TAN DELTA TEST OF BUSHING CT
6.SFRA TEST- SWEEP FREQUENCY RESONANCE TEST
7.BDV- BREAKDOWN VOLTAGE TEST
8.RATIO TEST
9.INSULATION RESISTANCE TEST
10.STABILITY TEST
11.HIGH VOLTAGE IMPULSE TEST
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gokulkrish
The General test conducted on transformer is
Open circuit test
Short circuit test
Double voltage and double frequency test
High Voltage test
| Is This Answer Correct ? | 0 Yes | 1 No |
Differentiate between Low and High impedance Protection
1 KVAR = 1.3Amps but, 25KVAR capacitor/690V capacitor takes just 21Amps as leading current, what is the reason? Please explain...
What is the secondry voltage of 420kV Current Transformer , the rated current is 2600A
What is the power factor you maintain at ur organization?
43 Answers Cummins, Exide, Johnson and Johnson, KTC, Microsoft, Powergear, Secure Meters, Suncity Strips, Wheels India,
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
IN PLATE EARTHING , PLATE LAID IN VERTICAL POSITION ,WHY HORIZONTAL WHY NOT
can we use 7volt DC BATTERY to run a 60watt motor by stepup? Give reason for your answer?
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
how we identify AC or DC machine at the time of seeing, with out use of name plate?
what is RR number Abbreviation energy meter
what is relation between vector group of transformer and its load hormonics?
What is meaning of Float Charging of Batteries???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)