what is general test conduted by transformer
Answer Posted / arya anup
mainly open circuit,short circuit test in order tomeasure
core loss & copper loss. then megger test to check the
insulation level between lv & HV coils.next is high voltage
test to measure capability to withstand impuse of very high
voltages( about 28kV will be applied between HV & Earth)
Then coms double voltage and double frequency test,where
we apply double the rated voltage on to the lv side with
100Hz frequency. this helps to find out insulation problems
between phase to phase.(All tests should be done with oil
inside only)
Oil also to be checked for its break down voltage(shold
with stand minmum 30kV)
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
RESPECCTED SIR/MADAM- I AM PRERING FOR SECTION ENGINEER (ELECTRICAL) RRB CHANDIGARH PLEASE SEND ME SOME PREVIOUS YEAR QUESTION PAPER OR MODEL PAPER.MY EXAM IS ON (30- NOVEMBER 2008).I AM VERY THANKFUL TO YOU. FROM- HARENDRA SINGH YADAV
why is control bus bi-directional?
Why should we hire you over the others waiting to be interview?
what are the 4 rules to start the motor?
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
how unidirectional torque is produced in DC motor?
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
what are the differant std sizes of cable trenches?
what happens in the short circuited secondary transformer,if the resistance of the short circuit is increased gradually?
What current flows in the transformer primary when its secondary is open?
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??
What is the resonant peak?
How many types of circuit loads are there in a common electrical circuit?
What Is Connection APFC Panel In Compony.
What are the various kind of cables used for transmission?