Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Procedure for conduting vector group test on power
transformers.why it is conducted?

Answers were Sorted based on User's Feedback



Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / maheshreddy

Purpose: The Polarity and Phase relation tests are
importent when two or more transformer are to be
paralleled.Parelleled transformer must have the same
polarity and phase relation to avoid parial or complete
short circuits.

Test Procedure:(Yyn11)
The L.V. vector will be superimposed on H.V. by connecting
1U & 2U Terminals. The three-phase voltage will be applied
to the line terminals of H.V. winding. Voltage measurement
will be done across:
1U-1V:
1V-1W:
1W-1U:

1V-2V: 1V-2W:
1W-2V: 1W-2W:
1U-2N: 1V-2N:



Checks: - 1V-2V = 1V-2W
1W-2V > 1W-2W
1U-2N + 1V-2N = 1U-1V

Is This Answer Correct ?    41 Yes 14 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / pavan

Vector group analysis is done to know the phase displacement.

Is This Answer Correct ?    17 Yes 5 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / suresh kumar

I also wanted to know this. But as per my knowledge, Same
phase of both primary and secondary are to be shorted
before applying voltage in the answer given by Mr.
Maheshreddy.
Please let me know am I correct?

Is This Answer Correct ?    14 Yes 5 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / gunasekaran

this is important for parallel operation vector group should
be same another one is vector group is changed polarity of
the transformer also change it YNyn0 become YNyn6 if it is
changed

Is This Answer Correct ?    6 Yes 1 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / r. n. aggarwal

It is conducted to ascertain the polarity and phase
displacement.

The polarity of two transformer having the same vector
group must be same.

A further check to confirm that the polarity or phase
displacement ( vector group ) of two transformer is the
same.A single three phase LT supply is fed to the HT side
of Transformers and the same phase of the LT suppy must be
connected to the corresponding HT terminals of
Transformers .Then the voltage is checked on LT terminals
of transformers with multimeter between the same phases and
it should read almost zero.

Is This Answer Correct ?    3 Yes 0 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / anil k panjani

I would like to know the test procedure for Dyn11 vector
group and the conditions to be met for the same

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

the fuse is use for protection against overcurrent but at normal condition it carry the rated current then how single thin wire carry this current without melting

1 Answers  


want happens when a dc is given to a commutator

2 Answers  


why current is constant on d.c?

0 Answers  


what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line

0 Answers   Jindal, Power Grid,


why single induction motor is not self starter?

3 Answers  


WHY WE NEED AUTO TRANSFORMER,WHERE WE CAN USE?

5 Answers   L&T,


how to interlock 2 incomer,1 buscoupler MCCB,like we interlock an ACB... pls answer this question and if possible send me the ckt diagram..

2 Answers  


diff between UPS and inverter?

2 Answers  


types of arc quenching methodes

2 Answers  


what is the merz prodution ? what is the turn to turn fault?

2 Answers   L&T,


How Arc Extinguish in Minimum oil circuit breaker and What is the function of Radial and axial vents of turbulator in Minimum oil circuit Breaker Where these vents are exists.

1 Answers  


hoe we can exlain the effect of caoacitor in fans????????

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)