if we convert kw into kva,which one formula use by us,pls
tell me?
Answers were Sorted based on User's Feedback
Answer / mohammed hussain a
Power in KVA = (1.732 * V in Volts * I in Amps)/1000*PF
For 3 Phase Supply
Power in KVA = (V in Volts * I in Amps)/1000*PF For 1
Phase Supply
or
KVA = KW/PF
| Is This Answer Correct ? | 34 Yes | 7 No |
Answer / r.muthu kumar
Killo Watts When KVA is knomw = KVA X Power Factor
Killo Watts 3 Phase = (I X V X 1.73 X P.F.) / 1000
Killo Watts 1 Phase = (I X V X P.F.) / 1000
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / parvez ahmed
For 1KW=1.25KVA
So...
PF=.8
1KW
KVA=KW/PF
=1/.8
=1.25KVA
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / kanth
actually
kw= vicos$
and
kva= vi
so KW= KVA/Cos$
cos$=KW/KVA
or
KVA=root of (Kw sq +KVAR sq)
| Is This Answer Correct ? | 6 Yes | 1 No |
For 3phase supply
KW= 1.732VIcosQ
KVA=1.732VI
for 1phase supply
KW=VICosQ
KVA=VI
if KW givwn means
KVA=KW/CosQ
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ravinder
AS PER THE PRACTICAL ASPECTS CONSIDERING PF
PRACTICALLY ....FOR 50 HP MOTOR WE HAVE TO TAKE 37.5 KW
(I.E. FOR 100 HP WE ARE TAKING 75 KW)......
| Is This Answer Correct ? | 1 Yes | 0 No |
what will happen if field winding of Synchronous generators given ac supply
What is the output voltage of a DG set.
How energy is generated in hydroelectric power plant?
If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.
what are the difference between protection class CT and Class PS CT
what are the oils used in transformers cooling? n which type transformer is used in power systems?
How to calculate the size of earth cable to earth the neutral of UPS ?
differentiate between remote backup relay and local backup relay?
Why grounding is generally done in supply end?
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
can we make a loop between neutral and body for grounding?
why we are not earthing ht cable at both the ends(sending & receiving end)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)