if we convert kw into kva,which one formula use by us,pls
tell me?
Answers were Sorted based on User's Feedback
Answer / mohammed hussain a
Power in KVA = (1.732 * V in Volts * I in Amps)/1000*PF
For 3 Phase Supply
Power in KVA = (V in Volts * I in Amps)/1000*PF For 1
Phase Supply
or
KVA = KW/PF
| Is This Answer Correct ? | 34 Yes | 7 No |
Answer / r.muthu kumar
Killo Watts When KVA is knomw = KVA X Power Factor
Killo Watts 3 Phase = (I X V X 1.73 X P.F.) / 1000
Killo Watts 1 Phase = (I X V X P.F.) / 1000
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / parvez ahmed
For 1KW=1.25KVA
So...
PF=.8
1KW
KVA=KW/PF
=1/.8
=1.25KVA
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / kanth
actually
kw= vicos$
and
kva= vi
so KW= KVA/Cos$
cos$=KW/KVA
or
KVA=root of (Kw sq +KVAR sq)
| Is This Answer Correct ? | 6 Yes | 1 No |
For 3phase supply
KW= 1.732VIcosQ
KVA=1.732VI
for 1phase supply
KW=VICosQ
KVA=VI
if KW givwn means
KVA=KW/CosQ
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ravinder
AS PER THE PRACTICAL ASPECTS CONSIDERING PF
PRACTICALLY ....FOR 50 HP MOTOR WE HAVE TO TAKE 37.5 KW
(I.E. FOR 100 HP WE ARE TAKING 75 KW)......
| Is This Answer Correct ? | 1 Yes | 0 No |
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
What are the protection schemes used for protection of transformers ?
3 Answers Engineers India Limited,
What is the difference between MCCB and MCB ?
Explain why the Voltage drop will happen in 3 Phase line?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
Can we put 3 layers of cable tray while installing tray
What is Generator Protection & Transformer Protection?
Difference between stepper motor & induction motor.
draw vector diagram and +ve,zero sequence diagram of symmetrical three phase fault.
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
which is better 50 HZ supply or 60 HZ supply?
Do you know how to maintain a generator, if so what are those maintenances?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)