why 4-20 mA signal is preferred over a 0-10V signal

Answers were Sorted based on User's Feedback



why 4-20 mA signal is preferred over a 0-10V signal..

Answer / satishpatel

the signal are transmitted from the field to the
controlroom and vseversa through cables. for long
transmission the cable resistance increases.thus if 0-10v
are transmitted over this long distance,due to the
resistance of cable there will be drop in the voltage and
the signal received at the controlroom will not be
accurate. to overcome this difficulty 4-20ma signal is used
for transmission.

Is This Answer Correct ?    286 Yes 24 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / ibrahim s

4-20mA :-
1. Easy to find the open circuit.
2. Less noise interference.
3. Current measures remain same in any point of the signal
line.

0-10V :-
This not able to fulfill the above criteria.

So that 4-20mA is preferred over 0-10v

Is This Answer Correct ?    115 Yes 10 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / supratim samanta

If 0-10 mA is used instead of 4-20mA then there will be
difficulties in error detection.Such as if there is any
fault is the transmission lines..we will never know,wheather
the indicated 0mA current corresponds to the initial
value(calibrated) of the measurement or it is due to fault
in transmission lines.

Is This Answer Correct ?    120 Yes 24 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / ibrahim s

0-10V :-
1. Voltage droup occurs.
2. Not able to find open circuit(Normally the circuit in
open condition o/p is "0", In 0-10V signal level starts
from 0V itself, so that can not able to find open circuit
easily)
3. Noise interference is high.

4-20mA :-
1. Easy to find the open circuit(because this signal level
starts from 4mA, if the circuit in open the output shows
0mA, so we can find easily the open circuit) .
2. Less noise interference.
3. Current measures remain same in any point of the signal
line.


So that 4-20mA is preferred over 0-10v

Is This Answer Correct ?    86 Yes 7 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / akg d gr8

Voltage drops due to Resistance and so we are using 4-20 mA

Is This Answer Correct ?    77 Yes 11 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / banibrata

In case of voltage transmission(here 0-10V)
1.there will be voltage drop along the transmission wire.
2.if we use 0 volt then we will be unable to find whether
the obtained 0 volt output is really the system output or
its due to instrument error.So for "live zero" concept we
need to give a particular value(other than zero) in the
lower range value.
3.Capacitive and magnetic effect due to voltage
transmission will be more than that in case of current
transmission.
4.2-wire transmission is not compatible with voltage
transmission.

But in case of 4-20 mA signal the above problems are solved.
1.In series transmission same current flows through the
ckt.So no current drop occurs.
2.Here the lower range value is 4 mA.So we can easily
detect after looking at the o/p whether the instrument
error occurs or not.In case of instrument error zero
reading will be shown.
3.2-wire transmission is compatible with it.

Is This Answer Correct ?    52 Yes 5 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / a.muthu kumar, vacon

In industry, the distance from controlroom
and the field is too long. If we use 0-10v signal
for feedback means voltagedrop will occur because of the
resistivity. So, 4-20mA is preferred instand of 0-10v
signal.

Is This Answer Correct ?    27 Yes 5 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / elsayem

in 4- 20
we can find if the process variables give zero because zero
is indicate 4ma
but in 0 - 10 if the process give zero we can not know
because the signal also 0v

Is This Answer Correct ?    22 Yes 11 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / luki satria

4-20mA can be easily detected for find a minimum and maximum
level measurement. in in 0-10 V some noise if we are not
prepared measurement

Is This Answer Correct ?    9 Yes 5 No

why 4-20 mA signal is preferred over a 0-10V signal..

Answer / shahaji shelke

To troubleshoot the loop or transmission signals,if voltage
signals is used it is difficult to troubleshoot due to it's
non linear properties as well as it's voltage drop within
the transmission,but due to linear current properties it is
easy to troubleshoot the transmission signal or 4-20 mA
signal.
Due to this the 4-20 mA is used in signal transmission.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

please send the hpcl (instrumentation) model placement papers to my mail....

9 Answers   HPCL, Invensys, IOCL, ONGC,


Reasons for using current as signal

1 Answers  


how the presure switches are calibrated? and what happen inside?

1 Answers  


what are the inputs (drawings) we need to prepare loop schematics??

1 Answers  


what is plc? Basic function of plc? application of plc in industry? What is lader diagram ? What is the main advantage to use plc in industry?

15 Answers   Schlumberger,






What is pre-commissioning and commissioning ?

1 Answers   Armco,


which processor is used in dcs.

0 Answers   ABB, Wave Distillery,


why we connect digital multimeter in series for dc current measurement and parallel for dc voltage measurement.

4 Answers  


what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?

0 Answers  


Ple give me "INDUSTRIAL INSTRUMENTATION AND CONTROL S.k. Singh 3th edition" Solution manual to self-Check Quiz and chapter-wise PowerPoint Slides. Home web-site not available... Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Thanks for all...

0 Answers  


why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.

0 Answers  


In instrumentation standard we use 4 to 20ma for transmission , why cant we use 3 to 19ma ?

1 Answers   NSH,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)