Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How can we check Zero of DP type Level Transmitter onside?

Answers were Sorted based on User's Feedback



How can we check Zero of DP type Level Transmitter onside?..

Answer / vijay

close the hp and lp valve and drain the water then open the
vent valve it should show the zero value.

Is This Answer Correct ?    15 Yes 6 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / jayaram

1.close the both HP and LP rootvalves
2.open the both HP and LP drain valves to drain the service
completely.
3.Close the drain valves.
4.open the vent caps of both HP and LP leadlines near the
rootvalves.
5.fill the lead lines completely with water.
6.obviously LP side , more pressure acts and current goes
below 4mA. So elevate the Zero Potentiometer to 4 mA(this
is for analog standard dp transmitter).
7.first of all you have to calibrate the dp transmitter for
the required range, then only you can do this elevation
zero checking.

Is This Answer Correct ?    11 Yes 8 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / altamash

close the both valve ie LP & HP then drain the water and then open the vent of LP then connect the HART and do the zero trim by HART then we can find ZERO

Is This Answer Correct ?    6 Yes 3 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / vishal

Just open the equilizer valve and u will get zero
No need to open or close any other valve
Check by multimeter

Is This Answer Correct ?    3 Yes 1 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / suresh agravat,jamnagar

first close the rootvalve then drain trhough needle velve
then close both LP and HP isolated valve and open equliser
valve

Is This Answer Correct ?    3 Yes 4 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / muhammad yasir

close HP isolation valve open HP side drain valve.Transimiter read maximum Differential pressure and Transimiter show O% Level or 4ma because LP lmpluse line liqued act pressure on LP side Transimiter.
When span check close both HP and LP side valves and open drain valve Transimiter read 0 differential pressure.Transimitter show 100% level or 20ma.

Is This Answer Correct ?    1 Yes 2 No

How can we check Zero of DP type Level Transmitter onside?..

Answer / faiyaz ahmad

first open the equalizing and then close the isolation valve and open the vent valve both side and make it zero in this condition transmitter will show zero.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

why we set -10 volt in vibration sensor output,why not +10 volt

3 Answers   GE, Honeywell, LLM,


pressure gauge measure static pressure or dynamic pressure?

3 Answers  


what is skin thermocouple?

3 Answers  


why using 4-20ma not using 0-20or why not using 1- 20ma???????

7 Answers  


What is calibration?

6 Answers   Syscon,


In which principles tx ,pressure gauge,Temp gauge,control valve works?

0 Answers   Bajaj, Professional Instruments,


How is SmartPlant Instrumentation related to INtools?

4 Answers   TCS,


What is super thermocoupal?

0 Answers   Emco,


difference between vaccum and draft

0 Answers  


which type of rtd is good for any system,2wire,3wire or 4 wire

9 Answers  


how do i calibrate mmwc pressure guage with out calibrator.if any? pls give me the ans.

1 Answers  


I want to measure level under vaccum by using DP Tx and vaccum vary between -500 to -670 mmHg and process fluid is accetic anhydride if consider process fluid density 1 kg/cm2. how to calibrate Tx ? consider level is 0 to 100 Cm.

1 Answers   CCC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)