Answer / jayaram
1.close the both HP and LP rootvalves
2.open the both HP and LP drain valves to drain the service
completely.
3.Close the drain valves.
4.open the vent caps of both HP and LP leadlines near the
rootvalves.
5.fill the lead lines completely with water.
6.obviously LP side , more pressure acts and current goes
below 4mA. So elevate the Zero Potentiometer to 4 mA(this
is for analog standard dp transmitter).
7.first of all you have to calibrate the dp transmitter for
the required range, then only you can do this elevation
zero checking.
| Is This Answer Correct ? | 11 Yes | 8 No |
Answer / vishal
Just open the equilizer valve and u will get zero
No need to open or close any other valve
Check by multimeter
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / suresh agravat,jamnagar
first close the rootvalve then drain trhough needle velve
then close both LP and HP isolated valve and open equliser
valve
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / muhammad yasir
close HP isolation valve open HP side drain valve.Transimiter read maximum Differential pressure and Transimiter show O% Level or 4ma because LP lmpluse line liqued act pressure on LP side Transimiter.
When span check close both HP and LP side valves and open drain valve Transimiter read 0 differential pressure.Transimitter show 100% level or 20ma.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / faiyaz ahmad
first open the equalizing and then close the isolation valve and open the vent valve both side and make it zero in this condition transmitter will show zero.
| Is This Answer Correct ? | 0 Yes | 2 No |
why t/c is connected parallel and what is the purpose of it
what is compensation? temprature & pressure
Control valve question what is the meaning of cauge.?what is the use of cauge?
Specific gravity.
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
it is possible to check the fail safe condition in pressure transmitter. if possible how?
Derive capacitance to 4-20ma conversion formula / relation in capacitance type pressure sensor?
why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &how to sloves this problem.
how micro-processor and micro controller different from architecture
3 Answers Bhushan Power Steel,
What is three element drum level control system why its better than single element?
I will attend an interview with GasGas company for a position of Instrument Technician ( Offshore )in next month can anyone tell me what questions they will ask. Thanks in advance.
What is inside the PLC panel? How does instruments communicate to DCS computer via PLC? What is the type of wiring in PLC connections? Please answer... Thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)