1. how much normal earth resistance in earth pits(neutral
and body earth) and transformer neutral and body earth &
panel earth.

Answers were Sorted based on User's Feedback



1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / rr0505

Earth resistance of earth pits shall depend on the terrain
in which the same is provided. Accordingly, based on soil
resistivity data of the location, no. of earth pits is
determined to ensure Grid earth resistance value below 5
Ohms for electrical grids,

For solidly grounded neutral of transformers, resistance
between Neutral & Body earth as well as panel earth shall
be zero.

Is This Answer Correct ?    124 Yes 24 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / rvg.msceb

The earthing resistance indicates the easiness of providing
a path. It should be as low as possible. Different
countries having standard values. In india, for commertial
applications its <1 ohm, and for railway its< 0.5 ohm.
for air craft and ships temp. earthing <10 ohm.etc.

Is This Answer Correct ?    82 Yes 8 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / shri6181

even any earth pit is concidered every earth pit should have the value 0ohms.but in rare cases u will get that value,more over will come 0.3to 0.9,there fore the earth pit value should be less than 1 ohm.ok

Is This Answer Correct ?    68 Yes 9 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / sanjay

NUETRAL&EARTH BETWEEN VALUE IS 0. AND TRANSFORMER BODY
EARTH AND NUETRAL BELOW 1OHM,ANDRESPECTIVELY PANEL EARTH
ISALSO BEBELOW 1OHM.

Is This Answer Correct ?    76 Yes 38 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / dinkar holmukhe

less than 1 Ohm

Is This Answer Correct ?    23 Yes 1 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / lion awan

0.5 to 1 Ohm is standard in my country

Is This Answer Correct ?    11 Yes 0 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / rakesh

For grid resitance it should be less than 5 ohms and for
indipendent earth pit it should less than 2 ohms.

Is This Answer Correct ?    51 Yes 42 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / kalpesh

earthing resetens 1 ohm to 3 ohm in rainy sesion only 1 ohm &other sesion aprox 3 ohm

Is This Answer Correct ?    9 Yes 3 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / kalpesh

Earth pit resistance 1.4 TO 1.6 NORMAL CNDITION

Is This Answer Correct ?    11 Yes 6 No

1. how much normal earth resistance in earth pits(neutral and body earth) and transformer neutral ..

Answer / nandakumar.r

Earth pits resistance was 0 ohms.due to soil difference its
vary slightly near 2 ~ 3 ohms.But its acceptable level in
our country.

For transformer neutral and body earth and panel resisteance
was zero ohms.

Is This Answer Correct ?    13 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

explain comutator action in detail.thanks

0 Answers  


Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?

0 Answers  


Do inductive loads have distorted current waveforms ?

0 Answers  


why a single phase induction motor has poor power factor

0 Answers  


How will change the frequency in distribution side?

0 Answers  






What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain

5 Answers  


how to compare with Relay settings for HT&LT panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps

0 Answers  


Which types of gate insttaled in static switch. Please give me answer.

0 Answers   cpgn,


How to check the Bushings of the transformer?

0 Answers  


pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..

0 Answers  


Why do u join toreent power ?

1 Answers  


What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)