Answer / prasanna d nerkar

Transformers are classified as two categories: power
transformers and distribution transformers.
Power transformers are used in transmission network of
higher voltages, deployed for step-up and step down
transformer application (400 kV, 200 kV, 110 kV, 66 kV,
33kV)
Distribution transformers are used for lower voltage
distribution networks as a means to end user connectivity.
(11kV, 6.6 kV, 3.3 kV, 440V, 230V)

Is This Answer Correct ?    216 Yes 31 No

what is the difference between power and distribution transformer?..

Answer / ashok reddy, r

power transformer generally operated at full load. Hence,
it is designed such that copper losses are minimal.
however, a distribution transformer is always online and
operated at loads less than full load for most of time.
Hence, it is designed such that core losses are minimal.

Is This Answer Correct ?    125 Yes 5 No

what is the difference between power and distribution transformer?..

Answer / hardik vyas

the main difference between power and distribution
transformer is, distribution transf. is designed for max.
efficiency at 60% to 70% load as normally doesnt operate at
full load all the time. Its load depends on distribution
demand. Where as power transf. is designed for max. effi.
at 100% load as it always runs at 100% load being near to
generating station.

Is This Answer Correct ?    124 Yes 14 No

what is the difference between power and distribution transformer?..

Answer / pundlik m wanwe

as per the design is concerned 1)the flux density is higher
than the distributin transformer.
2) power transformers are normally having higher voltage
(KV)and capacities (KVA).
3) Power transformer are so designed that they will have
Max. efficency at rated full load and the distribution
transformers will have max. efficency at 50% loading.

Is This Answer Correct ?    29 Yes 6 No

what is the difference between power and distribution transformer?..

Answer / muhammad shoaib

power transformers are designed so that copper losses be
minimum and distribution transformer are so designed so that
iron losses be minimum.

Is This Answer Correct ?    8 Yes 1 No

what is the difference between power and distribution transformer?..

Answer / uma sanker dwivedi

POWER TRANSFORMERS ARE INTEGRAL PART OF TRANSMISSION SYSTEM
HOWEVER DISTRIBUTION TRANSFORMER ARE PART OF DISTRIBUTION
SYSTEM.

Is This Answer Correct ?    20 Yes 16 No

what is the difference between power and distribution transformer?..

Answer / kaleem

Both power and distribution transformers are used for T&D
applications (transmission & distribution). The difference
between power and distribution transformers refers to size
& input voltage. Distribution transformers vary between 25
kVA and 10 MVA, with input voltage between 1 and 36 kV.
Power transformers are typically units from 5 to 500 MVA,
with input voltage above 36 kV.

Is This Answer Correct ?    29 Yes 26 No

what is the difference between power and distribution transformer?..

Answer / shvetang dave

Power Transformer are used for step up purpose from
trnasmission station to distribution station. Normally from
750 KV to 11 KV it is to be used. It is design for only I2R
losses b'coz Iron losses are constant b'coz it is operated
for constant application.

Whereas distribution Transformers are used for step down
purposes b'cos it is used for distribution purposes. It can
be used for Factory's required power as well as in society
it can be used for home's use. It can be used for 11 kv to
230 Voltage purposes. It can be Design for iron losses
b'coz It is operated for 70 to 80% operation so I2R losses
are not so much important

Is This Answer Correct ?    7 Yes 4 No

what is the difference between power and distribution transformer?..

Answer / poly20

Those transformers installed at the sending or receiving end of long high-voltage transmission lines are the power transformers.
Find more at below -
http://www.polytechnichub.com/difference-power-transformers-distribution-transformers/

Is This Answer Correct ?    2 Yes 0 No

what is the difference between power and distribution transformer?..

Answer / latika

Distribution transformers have LV side with 440/220V which
distributes the power to promises, shops, industries and
offices. So it is conventionally called distribution
transformer. 440V/ 220V are the Indian Standard dist.
voltage with 50HZ Freq. So in India transformer with LV side
having output of 440/220V is generaly called distribution
transformer. All others are power Transformer.

Is This Answer Correct ?    6 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What are the causes of motor vibration?

3 Answers   Equate,


Why front mounted CT polarities are always towards breaker?

0 Answers  


I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.

4 Answers  


Which type of power plant is more easier to produce electrical power at economical condition?

8 Answers   HAL,


do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042

0 Answers  






different between electrical and electronics Engineering????

4 Answers  


On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?

0 Answers   TNEB Tamil Nadu Electricity Board,


What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.

0 Answers  


What are the functions of different probes used in cro?

0 Answers  


Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..

0 Answers  


what is the type of starter used in tube light?

2 Answers  


what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?

1 Answers   Siemens,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)