Answer / prasanna d nerkar
Transformers are classified as two categories: power
transformers and distribution transformers.
Power transformers are used in transmission network of
higher voltages, deployed for step-up and step down
transformer application (400 kV, 200 kV, 110 kV, 66 kV,
33kV)
Distribution transformers are used for lower voltage
distribution networks as a means to end user connectivity.
(11kV, 6.6 kV, 3.3 kV, 440V, 230V)
Is This Answer Correct ? | 216 Yes | 31 No |
power transformer generally operated at full load. Hence,
it is designed such that copper losses are minimal.
however, a distribution transformer is always online and
operated at loads less than full load for most of time.
Hence, it is designed such that core losses are minimal.
Is This Answer Correct ? | 125 Yes | 5 No |
Answer / hardik vyas
the main difference between power and distribution
transformer is, distribution transf. is designed for max.
efficiency at 60% to 70% load as normally doesnt operate at
full load all the time. Its load depends on distribution
demand. Where as power transf. is designed for max. effi.
at 100% load as it always runs at 100% load being near to
generating station.
Is This Answer Correct ? | 124 Yes | 14 No |
Answer / pundlik m wanwe
as per the design is concerned 1)the flux density is higher
than the distributin transformer.
2) power transformers are normally having higher voltage
(KV)and capacities (KVA).
3) Power transformer are so designed that they will have
Max. efficency at rated full load and the distribution
transformers will have max. efficency at 50% loading.
Is This Answer Correct ? | 29 Yes | 6 No |
Answer / muhammad shoaib
power transformers are designed so that copper losses be
minimum and distribution transformer are so designed so that
iron losses be minimum.
Is This Answer Correct ? | 8 Yes | 1 No |
POWER TRANSFORMERS ARE INTEGRAL PART OF TRANSMISSION SYSTEM
HOWEVER DISTRIBUTION TRANSFORMER ARE PART OF DISTRIBUTION
SYSTEM.
Is This Answer Correct ? | 20 Yes | 16 No |
Answer / kaleem
Both power and distribution transformers are used for T&D
applications (transmission & distribution). The difference
between power and distribution transformers refers to size
& input voltage. Distribution transformers vary between 25
kVA and 10 MVA, with input voltage between 1 and 36 kV.
Power transformers are typically units from 5 to 500 MVA,
with input voltage above 36 kV.
Is This Answer Correct ? | 29 Yes | 26 No |
Answer / shvetang dave
Power Transformer are used for step up purpose from
trnasmission station to distribution station. Normally from
750 KV to 11 KV it is to be used. It is design for only I2R
losses b'coz Iron losses are constant b'coz it is operated
for constant application.
Whereas distribution Transformers are used for step down
purposes b'cos it is used for distribution purposes. It can
be used for Factory's required power as well as in society
it can be used for home's use. It can be used for 11 kv to
230 Voltage purposes. It can be Design for iron losses
b'coz It is operated for 70 to 80% operation so I2R losses
are not so much important
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / latika
Distribution transformers have LV side with 440/220V which
distributes the power to promises, shops, industries and
offices. So it is conventionally called distribution
transformer. 440V/ 220V are the Indian Standard dist.
voltage with 50HZ Freq. So in India transformer with LV side
having output of 440/220V is generaly called distribution
transformer. All others are power Transformer.
Is This Answer Correct ? | 6 Yes | 5 No |
What are the causes of motor vibration?
Why front mounted CT polarities are always towards breaker?
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
Which type of power plant is more easier to produce electrical power at economical condition?
do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042
different between electrical and electronics Engineering????
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
What are the functions of different probes used in cro?
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
what is the type of starter used in tube light?
what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?