Why the Transformer Nuetral is grounded?

Answers were Sorted based on User's Feedback



Why the Transformer Nuetral is grounded?..

Answer / prabhu gnanasekaran

In a distribution sector your fault current sector should
be immedietly earthed in order to sequre the equipment
getting damage. So the nearest path will be provided
through out the plant.
Transformer neutral is grounded because your transformer
will be the impotant electrical equipment and this has to
be protected for fault i cannot have a neutral floating and
it has to be earthed properly. It is also earthed in order
to reduce the 3rd Harmonics effect.

Is This Answer Correct ?    25 Yes 9 No

Why the Transformer Nuetral is grounded?..

Answer / infosys

neutral grounding transformers are used to derive a
neutral-to-earth connection for systems that do not
otherwise have one.

The grounding transformer can have a zigzag winding
arrangement, or a wye-delta arrangement.

The transformer primary terminals (wye side) are connected
to the power system, and its neutral is connected to earth,
perhaps through a controlled impedance. (Usually, with
Wye-delta grounding transformers, the impedance is connected
inside the delta.) No other load is connected to the delta
of the transformer.

These transformers provide a high impedance to normal
currents (positive & negative sequence), but allow ground
fault currents (zero sequence) to flow, thereby allowing
protective devices to operate if a ground fault occurs.

Is This Answer Correct ?    36 Yes 22 No

Why the Transformer Nuetral is grounded?..

Answer / swadesh

To give output voltage a reference.By grounding nutral we
put nutral on zero potential.

Is This Answer Correct ?    19 Yes 6 No

Why the Transformer Nuetral is grounded?..

Answer / amit

for earth fault
protection

Is This Answer Correct ?    8 Yes 5 No

Why the Transformer Nuetral is grounded?..

Answer / p_g

In practical cases the three phase voltages are not equal and there will be presence of potential at the neutral point and neutral is earthed to provide the path for unbalanced current during normal operation. The earthed neutral also helps during any abnormality in the system due to fault,it allows heavy currents to flow into the ground before the system isolated by means of protection system.

Is This Answer Correct ?    0 Yes 0 No

Why the Transformer Nuetral is grounded?..

Answer / ashok kumar mahato(junier elec

for balancing the load on the transformer and for testing the phase at any phase of 220 or 440 volts???????not in kv,,,

Is This Answer Correct ?    0 Yes 1 No

Why the Transformer Nuetral is grounded?..

Answer / bhaganna kolkur

When fault occurs in anyone of the phase then the fault current is increases 3 to 4 times more than the normal current so it will reduces voltage at secondry side.thise will affect the system (costly equipment) so to avoid thise neutral connection is done

Is This Answer Correct ?    4 Yes 7 No

Why the Transformer Nuetral is grounded?..

Answer / m fiaz javed

We are ground to neutral of a transformer because we give a
earth protection is opperate in any fault so we ground the
neutral of transformer.

Is This Answer Correct ?    0 Yes 6 No

Why the Transformer Nuetral is grounded?..

Answer / sachin_pawaskar2001

To earth circulating currents

Is This Answer Correct ?    8 Yes 22 No

Why the Transformer Nuetral is grounded?..

Answer / venkata suresh reddy

in this we can get sinsusiodal emf in 5limbed shell type and
3phase bank as well as we can supply single phase loads

Is This Answer Correct ?    4 Yes 18 No

Post New Answer

More Electrical Engineering Interview Questions

how to check avr of dg set of 125kva

0 Answers  


Differnce between negative Pahse SequenceFunction and unbalance Function?

0 Answers   Atsco, LMW Lakshmi Machine Works Limited,


what are the different types of transformers in present? which transformer is efficient?

1 Answers   TATA,


Why motor initial starting current is high?

9 Answers   Pennar,


what is the working principle of dc motor & its application ?

3 Answers  






how to reduce the power consumption in office ?

6 Answers  


while running ,synchronous generator is being turned off.what will happen to the current flow??

1 Answers  


As you achieve greater success with the company after some years, Will you like to be a share holder in our company?

0 Answers   PESPL,


please give me all the Alarm .Trip ,Safety Relays & Conditions of Chiller mail me on ashokbabunhce@gmail.com

0 Answers  


what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay

3 Answers  


along with technical test papers

0 Answers   Vee Technologies,


What is the lockout relay

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)