what is the difference between power and distribution
transformer?

Answer Posted / prasanna d nerkar

Transformers are classified as two categories: power
transformers and distribution transformers.
Power transformers are used in transmission network of
higher voltages, deployed for step-up and step down
transformer application (400 kV, 200 kV, 110 kV, 66 kV,
33kV)
Distribution transformers are used for lower voltage
distribution networks as a means to end user connectivity.
(11kV, 6.6 kV, 3.3 kV, 440V, 230V)

Is This Answer Correct ?    216 Yes 31 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is consequences of neutral and earth connect?

1667


What is center gravity load in substation?

1948


i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.

1871


Load transfer in 11kv double busbar switchgear - operation.

1508


Why front mounted CT polarities are always towards breaker?

1527






if any house we instaled a 1.5 ton ac and its phase cable of wiring is installed but netrual cable of wiring not instaed. my question is that is neutual of house(for other wiring is capable for ac load or a sepeart neutrual wiring required

1980


With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.

1517


what is the transformer turn ratio formula and give some examples?

1935


application s to shunt coil

1504


how to calculate the size of the HT cable

1429


How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.

2884


what happens to the water pump if ground water level is slowly decreasing?our water pump is varying from no-load full-load due to this problem

1224


Percentage losses in power generation?

2503


raleigh method

1654


Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA

1233