We know that,The air gap controls the amount of magnetic
field produced for a given current. In the equation
∫H·dL = n i , H is quite small in the iron because of its
high permeability. Nearly all of the integral accumulates in
the air gap even though the gap is very small compared to
the part of the closed path length in the iron. It reduces
the tendency of the iron to saturate to avoid harmonics in
the current.
thanking u
http://a2zengineering.blogspot.com/
z_hosen@yahoo.com
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / arockia doss.a
Actually the airgap in transformer is for transfer the
primary power to the secondary. Means the primary winding
input voltage level will be step up/down(Depends on type of
trf.) to the secondary winding.
This is exactly same with wats happening in a 3 phase ind.
motor between stator & Rotor.
Thats why we are calling ind. motor as "Rotating Trf".
Thanks ....
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / rakesh patel
It limits the short circuit current of the transformer and it also control the Saturation of the core.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / engr. kashif
None of the above answers gives a satisfactory explanation.....some1 plz elaborate it....Thanks.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nain
hi
air gap depend upon the applied voltage / range of voltage
in that gap.if it is not sufficient gap then breakdown of
the voltage will occur.
Is This Answer Correct ? | 1 Yes | 6 No |
Define load factor?
why we r using 4-20ma instead of 0-20ma in instrumentation
How RTCC panel is working and give single line diagram for RTCC with transformer?
What is the meaning of capacity of a 63 Amps TPN MCB? Is it the per phase capacity or the totol capacity?
What does impedance in the windings of transformer signify.
explain types of electric welding and its applications
What is voltage
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
How to calculate load taken by a cable?
Total power capacity of india at present
In a HT switchboard where Nos. of Transformers are connected, how to decide Incoming cable size? Whether Cable should be rated for connected load or maximum demand?
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?