Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

How to take Vector group test of Transformer?

Answer Posted / prasad talada

1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified

Is This Answer Correct ?    9 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What will be in Mahagenco Trade Test Exam? I want to know the same.

3645


what is the differences between microprocessor and general purpose computer

2115


if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)

1769


If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.

1047


how to determine the inrush current of a transformer

2557


Can a generator runs after getting 1st stator earth fault.

1357


what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.

1792


HOW WE CHOOSE EARTH'S POTENTIAL AS ZERO V?

2001


How do you determine the size of transformer radiators in a transformer?

1879


how we can do the insulation on secondary of ct explain and so that tan delta will within limit

1876


what is the function of bearing in dc mchine" and where it is placed

2526


in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?

2298


how we find transformer capacity by ohm

2134


1. what is usage for power factor in industries?? 2.why we need to monitor power factor??

8001


what is the condition for YnD11

2498