what is the method to measure the transformer current
carrieng capacity in three phase.
Answer / deepakindi1
same as u do in for any 3 phase circuits
ie KW=sqrt(3)*V*I*cos(@)
WKT cos(@)=KW/KVA
SO KW/cos(@)=KVA
KVA=sqrt(3)*V*I
I=KVA/sqrt(3)*V
FOR EXAMPLE CONSIDER 11KV/440V 100KVA TRANSFORMER
AT PRIMARY
I=100/sqrt(3)*11
I=100/(1.732*11)
I=5.24A
AT SECONDARY I=100/sqrt(3)*.44
I=100/(1.732*.44)
I=131.24A
Is This Answer Correct ? | 7 Yes | 4 No |
what is skin effect? why is it absentin dc system
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
What is the dependency of stiffness on load angle??
What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?
How i measured Bus bars weight without wighting ?
I am using submission of two ct in one and half scheme for 67/67N protection. Both CTs star point is grounded separately near ct box.Will two point ground give wrong tripping to 67/67N during fault or no matter.
What is the meager?
How to convert a two phase power into a three phase power in induction machine?
If i switch on a transformer but with no load connected to the secondary path.Is the transformer will burn?
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.