Do you know how to joint the H.T and L.T Cables?
Answers were Sorted based on User's Feedback
Answer / vinothbhabu
hello dear,jointing the cable not by using transformer or
by fevicol,and its not a simple like paper r wood jointing
by fevicol..
by using the heat strinkable method cable jointing will be
done,the heat strinking method gives high insulation to the
cable at jointing end,it can be used for jointing ht panel
board at the termination end,the kit used for the heat
strinkable is heavely insulation material,the joint will be
done by heating material...
for jointing the LT to LT cable above 6
sqmm,10,16,35,50,70,90,120,150,185,240,300,400,sqmm cable
by jointing the FERRULE LUG between the cable joint by
using cripping tools and then insulation tape will be
rounded it heavely......
Is This Answer Correct ? | 114 Yes | 17 No |
Answer / rvg.msceb
heat shrink joint is the best method. please check with
Rechem website.
No there is a new tehnology update that is Cold shrink
joint.
Is This Answer Correct ? | 37 Yes | 7 No |
The question is itself creating confusion. Are you asking
about the connection/jointing method,
or are you askinmg about the connection between HT-LT voltage?
Is This Answer Correct ? | 17 Yes | 2 No |
HT line tuns into LT by step down txr then connected lt
with LT cable
Is This Answer Correct ? | 24 Yes | 12 No |
Answer / pravesh
h.t. cables are joint by using h.v. straight througk joint
if it is cable and then heat shrink by using the
insulation .
l.t. cables are joint by using l.v. lugs and covered with
insulation and heat shrink or may be taken to H pole
structure to join with thimbles.
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / rajendra
to joint these cableslike L.T. & H.T. cables there are many
componyes are providing the jointing kit for low tansion
cable in that kit some insulating material,lugs,earthing
wire, past to fill in joint are avable and instrction
manual also avable with kit. so we must read the jointing
procidure in the instruction manual & use this material to
joint the cable.
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / mehul g. c.
you should not join h.t. & l.t. cables because both are used
for the different current rating & voltage rating.
if you are asking about connection then
1. for step up & step down the voltage you can connect to
the transformer.
2. for distribution you can connect to breaker.
or
if you are asking about jointing then it is not good but
1. you can joint by jointing kit. ( heat srinkeble ) as you
asked your cable is h.t & l.t it 3-core & more than 25
SQ.MM SO There is no other way to joint it.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / dilip b shah
H.T cable joint can be done by two method.
By Heat shrink kit or by m seal kit.If cable is unearth
prefere to use heat shrink kit. in earth cable prefere to
use m seal kit.
Two L.T Cable joint done by m seal kit(low voltage kit)
and end termination done by bimatalic lugs.
Is This Answer Correct ? | 22 Yes | 19 No |
Answer / mukesh kaushik
HT to LT can't be joined directly. So, interface used for
interconnection is Transformer.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / praveen
hi friends
ht and lt joints are not so easy
it need concentration and special care
first we should remove the area which was damaged
remove the sleeve and insulated material(ht cable)
use feruls and then crimp them with crimping tool
then use mastic tape to cover the feruls
next place the heat sink sleeves and heat them with
electric hot blower(hot air gun)
Is This Answer Correct ? | 1 Yes | 0 No |
what is power factor
What is the need of ISOLATION Transformer?
define transformer
What is the method of Tan delta test for power Transformes and why it is required.
list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
How to know the Max. current caring capacity of the cable by its size ?
is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?
Actually why the transformers are rated in KVA.?
iam using DM 3251 voltmeter(1 percent accuracy)for 11KV system PT ratio is 11KV/110V.can anybody explain what is the max and min voltage deviation.
If excitation will increase, then what will be the effect on power factor? Will it decrease or increase?
What is the function of an exciter in a generator?