What is a LBB protection and why it is used?
Answers were Sorted based on User's Feedback
Answer / monty
LBB called as a line breaker back up protection and it is used for the saftey of our equipment whenever fault occurs on line than the breaker of uper stream will be open if lower stream breaker will not operated.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / tpfasil200
Local breaker backup or breaker fail relay(LBB)..It is used when the trip command is given and the breaker fails to open due to some mechanical problem. The protection is time delayed and initiated by all trip conditions.On LBB operation, busbar protection is initiated, as all the breakers connected to that particular bus to which the circuit is connected have to be tripped.I t also trips the tie breaker and sends a direct trip command to the other end breaker.
| Is This Answer Correct ? | 4 Yes | 1 No |
Is it necessary to carry out sheath test after cable jointing? If the value is zero of such instance , is it ok to energize the cable?
actual rated capacity of a disc insulator??
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
why the value of impedence is taken as %impedence in fault currrent calculation
which is the best institute for PLC,SCADA,DCS in hyderabad
what is mind in cable
how many frequent start/stop operation possible in case of HT MOTORS.
which one is rotating transformer-single phase induction motor or 3 phase squirrel cage motor?
What are :- AC Distribution Board (Single & Double Front) DC Distribution Boards Distribution Board LT Breaker Panel.
Moving Iron instruments are applicable with a) DC only b) AC only c) DC & AC
14 Answers Bhel, Engineers India, Engineers India Limited,
Dear all i am kumaravel. now in chennai. my work is control and relay panel auto cad designing.up to 11kv to 400kv then question is i am improving my knowledge. i want some books name and auther are available for this C&R panel related. plese any one help me
What should be value of Circuit breaker operating time and tripping time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)