two TG running in parallel at equal load.one TG CB tripped
in reverse power relay.after tripping found its excitation
was on & turbine running at rated speed.Please clearify why
that TG tripped in reverse power ?
You have not mentioned whether there was increase in speed of the tripped TG. If not, at the time of tripping the load on it was zero or it was running as a motor .
| Is This Answer Correct ? | 0 Yes | 0 No |
WHAT IS LIGHTNING,HOW TO CALCULATE LIGHTNING DESIGN CALCULATION?
How many 2 ton window A/c can runs on a 125 KVA generator?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
Why there is restriction to generated voltage to certain limit for example (now 18kv) ?
3 Answers College School Exams Tests,
Q: How to calculate Transformer losses , tell us by Formula.
What is the formula to calculate the size of Aluminium and copper cable?
If we want to change a contactor of faulty one what are the conditions want to fullfil
Can any body tell me about partial discharge test, and why it is necessary and its procedure
125Kva Dg can take up how much amphere load.
in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?
how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)