in three 3.5 core aluminium ug cable. one cable is used for
one phase by shrting R,Y and B wires and other 2 cables
used for Y and b phases. balace 3 neutral wires are made
common and connected to load. suddenly neutral current was
more than line current what is the reason behind this?
The neutral current becomes more than the line current when the voltages applied to balanced 3 phase load , are not equal
| Is This Answer Correct ? | 0 Yes | 0 No |
explain why the secondary terminal of current transformer should not be lift open circuited.
How to connect a ELCB with contactor and relay ?
Star & delta kis principale pa hai.
how to carried out tan delta test in 11 KV alternator ?
can we share mvar in parrelell connected alternators
why we can turn on the phase-A scr in 3 phase converter at 30 degrees
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
What is fault.?
2 Answers AngloGold Ashanti, MNC,
In motors how many types of cooling systems were used?
is it possible to flow currnet between earth and nutral wire in a circuit???
What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)