CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE
IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND
TAKING OUTPUT FROM PRIMARY?

Answer Posted / akialok

during the design of power transformer,or any distribution
tfr the load current is taken into account ,and the windings
of the secondary side are accordingly designed that is the
load currents it can sustain ,insulation and cooling system
are taken into consideration...
suppose in your designing u r designed the windings to
sustain a 30 amp load current while reversing the windings
and taking the out put from primary as u stated, the load
current will be decreased at the 415 voltage side and the
current in the 220 voltage ll be increased to a factor of
transformation ratio as it has to work in same power..so the
windings of the 220 side may burnt out..if its not capable
of sustaining the increased current.

Is This Answer Correct ?    25 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to calculate fault level of 11 KV system

1524


Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)

1650


Explain the terms real power, apparent power and reactive power for ac circuits and also the units used.

641


How phase to phase voltage comes 440V.

1458


how we find transformer capacity by ohm

1745






generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...

1549


which type of cabel

1931


sir iam a 3rd yr eee student.no core company comes for recruitment to our college.my aim is to be placed in l and t.tell me the procedures.

1517


EXPLAIN USE OF ROCKING ARRANGEMENT IN ELECTRIC HEATING?

1387


What is the Surge for 1.1 Phase Induction Motor(For Eg.1Hp) 2.3 Phase Induction Motor(For Eg.1Hp) 3.AirConditioner(For Eg 1Ton) 4.Refrigerator(For Eg 180Ltr or 160kW) 5.Induction Cooker 4. Ceiling Fan

1630


how to calculate the change over time for star delta starter for different KW motor?

3754


Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode

1552


a starter used for squirrel cage induction motor?

1217


How to Make relay co ordination chart for a Electrical power distribution of a plant

3287


how is positive, negative, zero sequence is happen.. how is effect on 3 phase system

1295