Answer / vivek
A Valve positioner is employed to accurately position the
control valve at the proposed opening or closing position
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / welcome4ujd
Summary - Positioners
1. A positioner ensures that there is a linear relationship
between the signal input pressure from the control system
and the position of the control valve. This means that for
a given input signal, the valve will always attempt to
maintain the same position regardless of changes in valve
differential pressure, stem friction, diaphragm hysteresis
and so on.
2. A positioner may be used as a signal amplifier or
booster. It accepts a low pressure air control signal and,
by using its own higher pressure input, multiplies this to
provide a higher pressure output air signal to the actuator
diaphragm, if required, to ensure that the valve reaches
the desired position.
3. Some positioners incorporate an electropneumatic
converter so that an electrical input (typically 4 - 20 mA)
can be used to control a pneumatic valve.
4. Some positioners can also act as basic controllers,
accepting input from sensors.
A frequently asked question is, ‘When should a positioner
be fitted?’
A positioner should be considered in the following
circumstances:
1. When accurate valve positioning is required.
2. To speed up the valve response. The positioner uses
higher pressure and greater air flow to adjust the valve
position.
3. To increase the pressure that a particular actuator and
valve can close against. (To act as an amplifier).
4. Where friction in the valve (especially the packing)
would cause unacceptable hysteresis.
5. To linearise a non-linear actuator.
6. Where varying differential pressures within the fluid
would cause the plug position to vary.
To ensure that the full valve differential pressure can be
accepted, it is important to adjust the positioner zero
setting so that no air pressure opposes the spring force
when the valve is seating.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / nabakishore biswal
Positioner is an transducer which gives the proper position
of the final control element.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / aby
Positoner makes the control action very smooth. The usually
getting o\p is 3-15 psi. but it is not the exact pressure
required for the valve to operate it may be above this. so
we have to convert this standard pressure to a pressure
that is needed for the valve. this is done by the
positioner. Also by applying the signal to diaphragm only
it takes more time for the control action. so the
positioner makes a connetion with the step and the make the
action simple.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / raghuram
1) positioner name it self indicate as for accurate valve
positioning means for opening or closing for example: can
you please assume operator given 30% from HIS, of D.C.S,
WITH positioner accurately we can control valve position at
30% exactly ,with out positioner linearity is not posible.
2) At the time of calibration we will make linear 4 to 20
ma to .2 to 1k.g for I/P, but in case of positioner we will
check position(valve open close) with I/P, with valve
percentage for ex:
ma position(%)
4 0
8 25
12 50
16 75
20 100
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / cipriano
A valve Positioner is a device used to increase or decrease
the air pressure operating the actuator until the valve stem
reaches the position called for by the instrument controller.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anu
Positioner is for
1. amplification of 3-15 psi pneumatic signal from I/P
comvertor and the amplified signal ( eg. .2 - 1 kg/m2
range) is the i/p for the actuator.
2. feed back
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / praveen kumar
Positioner is used to Control valve for controlling the
final element, and where the signal is feeded to positioner
only the link is connected to Valve stem for opening &
closing.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / aallam
positioner convert 4-20 mA to 3-15 psi and by 3-15 psi control the supply air to the valve to open or close with help by feedback arm to correct the supply air to the vave
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mr.rao
It is doing sharing the signal(actual level)to Controller.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the square root flow transmitter formulla ?
What is critcal speed. what is resonant frequency. why we want to cross crtcal speed on higher RPM (early).
Why do you want to work here
what is instrument termination
what is function of SCADA , and how is it work, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
please send me the inteview questions in IOCL
Calibration of controller (pneumatic)
How to rerange a dp type level transmitter after installation?
How much flow is passing through 6 inch line? There are no gauge, no any transmitters in line.
all questions related to instrument technician in any offshore oil and gas company.
What is the differences of Level swich( LS ) and Level Transmitter(LT)
Hi i am aneesh, done btech in applied electronics & instrumentatiin. And then i took mba in finance & marketing.After that i got placement in finance co and worked there for 3.5 yrs.Now i wanted to come back to engineering job.But without engg experience, i may not able to find an opening.i have done a course related to flow meters and ite calibrations. Kindly suggest where should i try to get a job?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)