How can we say that accuracy of measurement increases by using 3 or 4 wire RTD?
because for example:
If resistance of RTD element is say r ohms and
Resistance of the cable from transmitter to RTD is R ohms
And if 4 wire RTD is used,
____._____________________ R ohms
|
|_____._____________________ R ohms
/
\
/ r ohms
\
\
|
|______.__________________ R Ohms
|
|_______._________________ R ohms
Then the actual resistance measured will be:
Total = r + R/2 + R/2 = r +R Ohms
Note: r+R instead of r ohms. hence error
Answers were Sorted based on User's Feedback
Your maths is not right but actually you are right, and the
temperature indication does not increase so significantly
that it is worth the effort to use a 3 or 4 wire RTD. It
might increase with something like 0,001Deg C so that is so
small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / kalla anil kumar,jeypore
Hi Friend
There will be small difference between 2wire,3wire and 4wire RTD, in 2wire if the Distance between RTD and Transmitter is so long then there will be adding of cable resistance so it will shows error reading for example in 2 wire RTD like PT-100 RTD and wire resistance 2ohms each 2wire x 2ohms so total resistance 104 ohms at 0deg,so to avoid the error in reading we can use 3rd wire to compensate the error,for example in 3wire RTD like PT-100 main wire 1 and reaming two wire are 2 & 3,then Tx will calculate total resistance in 1&2 wires it will be 104 ohms at 0deg, and in between 2&3 wire 4 ohms,so Transmitter will calculate 104-4=100 ohms at 0 deg, NOTE- lead cable resistance of RTD should be same from field to transmitter.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by nuclear power plant?
Explain ratio control system.
Good evening all I need a small favour regarding reliance paper i wanna probable sample papers(e&i) of reliance. if any of u have any idea about dis then plz mail me back.i belongs to electronics and instrumentation engg.so i need e&i papers. thanking u....
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
How to fix back the valve actuator stem
What is instrumentation amplifier?
Why Flow measurement has to use Square Root
what is the working principle of vortex flowmeter
What is mean by trim?
types of valves
3 Answers Bindal Papers, Kuwait Oil Company,
how to calibate level transmiter ?range -150 to +150.what is the zero and span?
wat are the interview questions asked in air india for post service engineer
1 Answers AirIndia, Shree Renuka Sugars,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)