How can we say that accuracy of measurement increases by using 3 or 4 wire RTD?
because for example:
If resistance of RTD element is say r ohms and
Resistance of the cable from transmitter to RTD is R ohms
And if 4 wire RTD is used,

____._____________________ R ohms
|
|_____._____________________ R ohms
/
\
/ r ohms
\
\
|
|______.__________________ R Ohms
|
|_______._________________ R ohms

Then the actual resistance measured will be:
Total = r + R/2 + R/2 = r +R Ohms

Note: r+R instead of r ohms. hence error

Answers were Sorted based on User's Feedback



How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example..

Answer / sam

Your maths is not right but actually you are right, and the
temperature indication does not increase so significantly
that it is worth the effort to use a 3 or 4 wire RTD. It
might increase with something like 0,001Deg C so that is so
small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck

Is This Answer Correct ?    7 Yes 0 No

How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example..

Answer / kalla anil kumar,jeypore

Hi Friend
There will be small difference between 2wire,3wire and 4wire RTD, in 2wire if the Distance between RTD and Transmitter is so long then there will be adding of cable resistance so it will shows error reading for example in 2 wire RTD like PT-100 RTD and wire resistance 2ohms each 2wire x 2ohms so total resistance 104 ohms at 0deg,so to avoid the error in reading we can use 3rd wire to compensate the error,for example in 3wire RTD like PT-100 main wire 1 and reaming two wire are 2 & 3,then Tx will calculate total resistance in 1&2 wires it will be 104 ohms at 0deg, and in between 2&3 wire 4 ohms,so Transmitter will calculate 104-4=100 ohms at 0 deg, NOTE- lead cable resistance of RTD should be same from field to transmitter.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is the working principle of hydra step(electronic level indicator)?

2 Answers   Bengal Energy, Lanco,


how to calculate the total flow in square root

0 Answers   PTI, Qatar Kentz,


why cant we use mV instead of mA?

12 Answers   ABB, Power Grid, Qatar Gas, USW, Visa Steel,


what is the input to be given in digital flow meter during the the calibration time?

0 Answers   ONGC,


For an Instrumentation Engineer, is there any effect on Instruments of safety zones like zone0, zone1, zone2. As an instrumentation Engineer, what we have to consider or remember while working in these areas.( zones 0,1,2).

1 Answers  






How to Calibrate Vortex Flow transmitter in field

0 Answers  


How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System

0 Answers  


What is Erosion in a control valve?

0 Answers   CCIE, Fisher,


1,why we use 4-20 ma output of all instrument qhy not use 0- 20, 2,what is the different between PLC & DCS. 3,how can we meaure maximum span of new flowmeter if not given any information.

4 Answers   Reliance,


how to explain PID?

2 Answers   Jindal,


i am preparing for BARC ,so plz mail me how to prepare for BARC. ALSO IF POSIBLE SOME RELATED QUESTIONS. MY MAIL ID IS khushi_4uall2003@yahoo.co.in

0 Answers  


Different between control valve and mov

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)