Answer Posted / welcome4ujd
Summary - Positioners
1. A positioner ensures that there is a linear relationship
between the signal input pressure from the control system
and the position of the control valve. This means that for
a given input signal, the valve will always attempt to
maintain the same position regardless of changes in valve
differential pressure, stem friction, diaphragm hysteresis
and so on.
2. A positioner may be used as a signal amplifier or
booster. It accepts a low pressure air control signal and,
by using its own higher pressure input, multiplies this to
provide a higher pressure output air signal to the actuator
diaphragm, if required, to ensure that the valve reaches
the desired position.
3. Some positioners incorporate an electropneumatic
converter so that an electrical input (typically 4 - 20 mA)
can be used to control a pneumatic valve.
4. Some positioners can also act as basic controllers,
accepting input from sensors.
A frequently asked question is, ‘When should a positioner
be fitted?’
A positioner should be considered in the following
circumstances:
1. When accurate valve positioning is required.
2. To speed up the valve response. The positioner uses
higher pressure and greater air flow to adjust the valve
position.
3. To increase the pressure that a particular actuator and
valve can close against. (To act as an amplifier).
4. Where friction in the valve (especially the packing)
would cause unacceptable hysteresis.
5. To linearise a non-linear actuator.
6. Where varying differential pressures within the fluid
would cause the plug position to vary.
To ensure that the full valve differential pressure can be
accepted, it is important to adjust the positioner zero
setting so that no air pressure opposes the spring force
when the valve is seating.
| Is This Answer Correct ? | 10 Yes | 0 No |
Post New Answer View All Answers
what is IEC code in cables & how to selecting cables?
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
Explain types of valves?
Full form of KKS when use DCS.
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
how to relay switch sense the fault?
What is the difference between working pressure and calibration pressure of a control valve
sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.
Explain the key components of control loop?
Can any body help to get Rsemulator 5000 free from internet if possible then give me any link or any help .
Explain about safety integrated level protection? . How it was differ from other protections ?
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
How many ohms are required for proper earthing?
IS there any effect of vortex in low pressure side of the transmiter after the orific in feed water line? if yes then what is the calculation?
what is exact time to study dcs and plc cources