Answer / krish

When a motor starting with star/Delta starter,In case of
Open transition during change over time from Star to Delta
for momentarily the supply will interupted for the motor &
it changes to Delta,But in case of closed Transition there
connect resistance will when change form star to delta &
this arrangement will avoid the open Interuption

Is This Answer Correct ?    10 Yes 1 No

Please explain open transition and closed transistion system in Star delta Starter?and also the st..

Answer / sashi kanth

COnsider a 3 phase induction motor is switched on by the
means of starter in delta configuration winding of stator.
This is usually done to reduce the time the machine takes
to run at rated speed as the voltage across each phase is
not V/1.732 = 230 V but is 415 V. During normal operation,
winding has to be converted to star configuration. This
transition can be done either by disconnecting the prior
configuration for some instant of time and connecting the
other configuration. As the machine is disconnected from
the excitation for some instant of time it is called open
transition. Closed transition of stator configurations is
done without losing the continuity of the excitation.
Refer to Control of electric drives by Bhattacharya and it
will be more clear.

Is This Answer Correct ?    8 Yes 3 No

Please explain open transition and closed transistion system in Star delta Starter?and also the st..

Answer / dave

worked for carrier a/c 35 years. in a standard open
trastion when charging from star to delta the motor
effectively slows momenatrily for a 1/5 of a scond. closed
traansition this does not happen ,the change from star to
delta is less noticeable.closed transiontion has a fourth
contactor and resistor bank to prevent that 1/5 of second
power loss to the windings .I need some wiring digrams of
closed transion staters to show the tecs how this works

Is This Answer Correct ?    5 Yes 0 No

Please explain open transition and closed transistion system in Star delta Starter?and also the st..

Answer / bala123

can any body please tell about the calculation for find
this resistance values??????????????????????????

Is This Answer Correct ?    2 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

three owners X, Y, z owned some tractors with them, on the first month x gave away the same amount of tractors to y and z ( as much as they possed), similarly in the 2nd month y gave of to x and z similarly by third month z gave to x and y. after this all X, Y, Z had 24 tractors each.

2 Answers   econ,


what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV

0 Answers  


what happen "when Dyn11 is parallel operation with Dyn1"?

9 Answers  


what is nuetral grounding

2 Answers  


Dear sir,how should i set the relay in star delta starter..say ex i am having 4ohp motor,,wht should be the relay setting...?

4 Answers  






Why are iron cores in transformers made laminated?

0 Answers  


What is meant by "tampering detection" of a electrical energy meter?

3 Answers  


Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?

1 Answers  


how to syncronize two dg sets

3 Answers  


what is the function of choke in tube

1 Answers  


63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?

0 Answers   GSECL, L&T,


what is the significance of tan delta testing?explain the theory?

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)