Please explain open transition and closed transistion
system in Star delta Starter?and also the state difference
of both?
Answer Posted / dave
worked for carrier a/c 35 years. in a standard open
trastion when charging from star to delta the motor
effectively slows momenatrily for a 1/5 of a scond. closed
traansition this does not happen ,the change from star to
delta is less noticeable.closed transiontion has a fourth
contactor and resistor bank to prevent that 1/5 of second
power loss to the windings .I need some wiring digrams of
closed transion staters to show the tecs how this works
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
is it possible to have dc motors on single chip
How test for Ddo vector group test condition?
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
how to compute kvar in substation feeder to improve power factor and sending voltage
what are the disadvantages in GIS over AIS
What is the permissable nutral current of three phase system as per IS standards?
dc supply given to dc generator winding.how is possible? my knowledge is saying the winding will burn. please reply.
How the circuit breaker is selected for Induction motor of 100 kW, 415 volt, 0.85 power factor, 0.95 efficiency ?
A d.c. Shunt motor is found suitable to drive fans because they require?
What are the advantages of skewing of cage rotor conductors?
Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.
What is resistance of 50meters, 16sq.mm, single core copper cable?
ACCORDING TO IEC WHAT SHOULD BE THE MINIMUM HEIGHT OF G.I. STRUCTURE OF CT, PT, ISOLATOR, LA?
two way ckt diagram can be drawn by how many ways? give diagram
What is the method of estamating of cable, CB,MCB ?