hw to calculate flc of motor ? data are:3-phase,50Hz,30kw
Answers were Sorted based on User's Feedback
Answer / chetan & panks
Please mention voltage level & PF.
Assuming the voltage level 415V & PF 0.85,
FLC=kw/(ROOT3xkVxcoso)
= 30/(1.74x0.415x0.85)
= 48.87A
| Is This Answer Correct ? | 52 Yes | 4 No |
Answer / pintoo
the data u have given is not sufficient to calculate the
FLC.
the exact formula to calculate FLC is:
P=sqrt(3)*V*I*cos(phi)*efficiency
I=P/[sqrt(3)*V*cos(phi)*eff.]
P=30KW=30000Watt
V=415V
cos(phi)=?
eff.=?
put the value of cos(phi) and efficiency then u will get
accurate FLC.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abhishek uppal
1H.P= 0.746 watts i.e power
so in 3 phase ,power =root3 *v*flc(Il)*cos phi
power =.746 watts
v=415v, and cos phi=0.8...so substituting above values
0.746=1.732*flc*415*0.8
so 7460/1.732*415*0.8= 1.31 A
So flc=1.31A...so accordingly,
find for 30 kw.
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / x man
i will tellu a simple method,
hpx1.4 ..its an industrial method
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / rajkumar r
U CAN FIND FLC OF THE MOTOR IN THE MOTOR NAME PLATE ITSELF.
MOREOVER,
1HP=0.746KW
1KW=1/0.746HP
30KW=30/0.746 HP=40HP
Practically current taken by 1HP motor=1.342A
so full load current of 30kw(40HP) motor=40*1.342=54A
| Is This Answer Correct ? | 20 Yes | 32 No |
Answer / adnan
FLC : Can be Measured By their name Plate
Engr.adnan
| Is This Answer Correct ? | 0 Yes | 13 No |
what is the calculation of current when a clampmeter is attached to two phases of any drives.
What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?
how meger function
One amps in HT is equal to how manys amps in LT
explain PV modules in solar energy generation.
an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
how to calculate P.F from kva only?
Where is the best place to mount distribution panel in a house.
0 Answers Wantro Technical Services,
I have motor of 3 H.P. How i found the rating of capacitor use in it in single phase motor..???
how do prepare ongc exam.how is it question model.i am electrical. which part covering in electrical.tell me
why make protection 85% of winding?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)