hw to calculate flc of motor ? data are:3-phase,50Hz,30kw
Answer Posted / abhishek uppal
1H.P= 0.746 watts i.e power
so in 3 phase ,power =root3 *v*flc(Il)*cos phi
power =.746 watts
v=415v, and cos phi=0.8...so substituting above values
0.746=1.732*flc*415*0.8
so 7460/1.732*415*0.8= 1.31 A
So flc=1.31A...so accordingly,
find for 30 kw.
| Is This Answer Correct ? | 8 Yes | 9 No |