hw to calculate flc of motor ? data are:3-phase,50Hz,30kw
Answer Posted / rajkumar r
U CAN FIND FLC OF THE MOTOR IN THE MOTOR NAME PLATE ITSELF.
MOREOVER,
1HP=0.746KW
1KW=1/0.746HP
30KW=30/0.746 HP=40HP
Practically current taken by 1HP motor=1.342A
so full load current of 30kw(40HP) motor=40*1.342=54A
| Is This Answer Correct ? | 20 Yes | 32 No |
Post New Answer View All Answers
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
what is meant by twilight switches 7 where its applicable ?
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
What is meant by short-pitched winding?
What is a system?
DG Earth Value?
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.
in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?
Do closed loops systems require manual input?
what is circuit breaker in transfomer and where it used
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
What is the diff. between single compression and double compression gland
What do you mean by pull of electromagnet?