HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF
IMPROVEMENT?
EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
Answer Posted / bala123
please mention the existing powerfactor....
| Is This Answer Correct ? | 30 Yes | 9 No |
Post New Answer View All Answers
i want to know how to determine that a surge arrester work properly in 11kv system. and how to test a 12kv surge arrester
What is the vector group of a transformer,how can it be found out?
If the feeder rating is 7.5 kw or 10 HP star-delta feeder, MCCB is taken as 63 a, contactors-32 a, how much will be the OLR rating or which range OLR should be considered when we concern about type-2 coordination?
What is sink and source?
what is meaning of bus riser
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
wheather the size of windings in motor and generator are the same
As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
Why we find the sensitivity for the CT's to check?
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
1. Design a counter which counts 0, 4, 8, 2, 6, and repeats using: 1.a using JK flip flops 1.b using T flip flops 1.c using D flip flops
How to Decide the Location of Earth pit for Compressor in Oil Depo? and How to measure the resistance of earth pit Pls explain me with the help of Circuit Diagram?
The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.
How to use computer cpu ups use for home inverter circuit board