Answer / suresh g
elcb means earth leakage circuit breaker which operates when
there is a leakage of current from phase to earth.
Rccb means residual current circuit breaker which operates
when there is a difference in current between any two
phases.This differential current is called resdual current.
Is This Answer Correct ? | 382 Yes | 85 No |
Answer / k.senthilkumar
ELCB:-An ELCB is a specialised type of latching relay that
has a building's incoming mains power connected through its
switching contacts so that the ELCB disconnects the power
in an earth leakage (unsafe) condition.The ELCB detects
fault currents passing from live (hot) to the earth
(ground) wire within the installation it protects. If
sufficient voltage appears across the ELCB's sense coil, it
will switch off the power, and remain off until manually
reset. An ELCB however, does not sense fault currents
passing from live to any other earthed body.
RCCB:-A residual current device (RCD), or residual current
circuit breaker (RCCB), is an electrical wiring device that
disconnects a circuit whenever it detects that the electric
current is not balanced between the phase ("hot") conductor
and the neutral conductor. Such an imbalance is sometimes
caused by current leakage through the body of a person who
is grounded and accidentally touching the energized part of
the circuit. A lethal shock can result from these
conditions; RCDs are designed to disconnect quickly enough
to mitigate the harm caused by such shocks.
Is This Answer Correct ? | 206 Yes | 20 No |
Answer / sabarikumar r
ELCB is a voltage operated device.RCCB is a current
operated device.IN ELCB, Trip coil is connected between
system ground and non current carrying part of the
machines.RCCB having CBCT(Core Balanced Current
Transformer).CBCT consists of 2nos of primary winding
(P1,P2) and one secondary winding(S1).Primary windings are
in series with the load and secondary winding connected to
Trip coil.In case of healty time, voltage in both the
primary windings will be cancelled and hence no voltage on
secondary winding.During the leakge or If any body touch
the live wires of the machines, current will passing
through the body and connected to ground.It will cause the
voltage difference in primary windings and induced voltage
in secondary operates the trip coil(operating time 50ms).
Is This Answer Correct ? | 220 Yes | 48 No |
Answer / sandy
ELCB has a protection for earth leakage where as the RCCB
has the dual protection features of ELCB and MCB
Is This Answer Correct ? | 273 Yes | 184 No |
Answer / anc
1)
An RCCB will disconnect if there is sufficient fault
current flowing from any part of the protected circuit to
any other path. An ELCB will only disconnect if there is
sufficient fault current flowing from a live part of the
circuit to the protective earth conductor.
2)
ELCBs are old hat.
3)
RCCBs are cool for compliancy purposes ELCBs are not.
4)
RCCBs are pretty good at protecting people against electric
shock. ELCBs are pretty crap.
5)
An RCCB disconnects a circuit when there is a difference
between the current in the phase side of a circuit and the
return side of that circuit and when this difference is
filtered and exceeds a threshold trip current value(In this
context ‘return’ for most purposes is the neutral conductor
but for some installations could also conceivably be
another phase connection).ELCBs work by detecting current
(or valtage induced by current) in the protective earth
conductor.
6)
It is difficult to see why anyone would choose to use an
ELCB over an RCCB given that an ELCB will only prevent the
protective earth conductor from reaching a dangerous
voltage under fault conditions. RCCBs will also do this and
more.
Is This Answer Correct ? | 52 Yes | 5 No |
Answer / vinod kumar
ELCB earth leakage circuit breaker
RCCB residual current circuit breaker which operates
when there is a difference in current between any two
phases.This differential current is called resdual current.
Is This Answer Correct ? | 74 Yes | 35 No |
Answer / monti
rccb:-it measures the difference in current between live
and neautral conductors of a system.in normal conditions it
is equal.If it is diff. than it indicates that some current
is flowing other than live and neutral
Elcb;-it measures the voltage on earth conductor.If this
voltage is not zero that indiacate a leakage to earth
Is This Answer Correct ? | 63 Yes | 25 No |
Answer / aqeeb
elcb means earth leakage circuit breaker which operates when
there is a leakage of current from phase to earth.
Rccb means residual current circuit breaker which operates
when there is a difference in current between any two
phases.This differential current is called resdual current.
Is This Answer Correct ? | 33 Yes | 8 No |
Answer / tulasi ram.k
ELCB:ELCB IS AN EARTH LEAKAGE CIRCUIT BREAKER WHICH CHEAK
THE LEAKAGE OF CURRENT TO THE EARTH AND TRY TO BREAK THE
CIRCUIT POWER.
RCCB:RCCB IS AN RECIDUAL CURRENT CIRCUIT BREAKER WHICH
CHEACK THE ELECTRICAL CURRENT DIFFERENCE BETWEEN TWO PHASES
IT WILL BREAK THE CICUIT POWER
Is This Answer Correct ? | 53 Yes | 30 No |
Answer / bad n
There are 2 types of ELCB ; voltage operated and current
operated. Current operated ELCB is RCCB or sometimes people
call RCD. Voltage operated ELCB have earth wire connect to
ELCB. It is for the ELCB to measure the leakage voltage and
will trip if the leakage voltage reach to dangerous value.
While RCCB (Current operated ELCB) monitor the different in
current between Neutral and Live(or phases). The
differential current is called residual current. RCCB will
trip if residual current reach at certain value depends on
rated RCCB sensitivity.
Is This Answer Correct ? | 31 Yes | 10 No |
what is principle of DC machines?
5 Answers APTransco, NTPC, Wipro,
What are the difference between these terms ? e.m.f, voltage, potential, potential difference, current etc? what are the difference between these terms ? (electromotive force) e.m.f, voltage, potential, potential difference, reference potential, reference potential difference, current. How can i explain and describe these all terms in single line each and little more explaination too thanks
Why do you get a typical sound when the transformer is put into operation?
Why DC Currents are not used in transformer?
is a normal conductor can be used a core in windings if not what is the winding core speciality.
why choke is provided in the centre of the tube light?
what is the Mechanism of energy saver FAN how average power,reactive power, power factor e.t.c realated to it and how it apply to this FAN .and how this fan save energy w.r.t circuit analysis,plz repaly to this question this is the assignment to given to me.thanks
WHAT IS THE DIFFERENT BETWEEN MCB & MPCB? & HOW IS USE?
what is the contact resistance of vacume circuit breaker??
What is the importance of counter based plan & how is it scheduled?
what will happen ac motor give to dc supply
9 Answers Areva, College School Exams Tests,
All we know about T/R, Is it possible to make T/R primery singlr phase and secondery three phase,If it then how?... Need Description