Answer / atul naik
Its not 100% true. Actually Motor has been protected many
a times before it actually burns. But either we have
ignored the actual reason of tripping by resetting OL
Relay or by removing the Over Load on Motor.
Still Motor Burns. So it is observed that following reasons
are there. 1 Dips in Supply Voltage, 2 Frequent Over Loads
reduces the performance/ sensitivity of OL Relay 3 Short
Ckt Protection is Not there (ANSI 50 & 50N )4 Short Ckt
Protection is Not Fast or delayed ( to avoid Nusence
tripping in Starting )5 Impairing of an Insulation due to
entry of unwanted gases,liquids etc,Reducing the Insulation
Strength of the Motor.,6 Wornout bearings, it will not only
oppose the motion and create resistance but also it
increases the heat / temp. 7 In case of CT Operated
Relays , CTs may reduce senstivity. Now, the cumulative
effect is that Fault Clearing Time is More than the Temp
rise time due to Fault , due to which Motor insulation
fails and motor winding no longer remain healthy ie Motor
burns.
| Is This Answer Correct ? | 19 Yes | 1 No |
What is thermal relay and how it is works in transformer please explain
If one lamp connects between two phases it will glow or not?
which type sylbuse involved
why vector group used in transformer and what effective in output
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
How can make a star delta with Rstar delta feeder ( ( 4contactor & one timer ) pls answer with digram (power &control digram)
Dear all i want to know SEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me zohairaukllah@yahoo.com
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
How to calculate the size of window A.C. for 200 Sq. ft room?
A 230 v dc series motor is connected to 230 V ac supply, then
how can we represne the analog signal and digital signal if want to measure the speed and we have to use PLC
hi , i have 150 kw loud and we need 50 m cabil,i want to know wich size cabil we use. thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)