Answer Posted / sabarikumar r

ELCB is a voltage operated device.RCCB is a current
operated device.IN ELCB, Trip coil is connected between
system ground and non current carrying part of the
machines.RCCB having CBCT(Core Balanced Current
Transformer).CBCT consists of 2nos of primary winding
(P1,P2) and one secondary winding(S1).Primary windings are
in series with the load and secondary winding connected to
Trip coil.In case of healty time, voltage in both the
primary windings will be cancelled and hence no voltage on
secondary winding.During the leakge or If any body touch
the live wires of the machines, current will passing
through the body and connected to ground.It will cause the
voltage difference in primary windings and induced voltage
in secondary operates the trip coil(operating time 50ms).

Is This Answer Correct ?    220 Yes 48 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to measure the earth resistance value in a concrete pavement(flood light area)?

1731


What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.

1333


Can we test the alignment of End shield and stator of turbogenerator without rotor insertion? Also how to fix maintain the alignment at site installation?

1798


What happened when voltage will half value of current ...

1126


HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.

1764






what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line

2871


Leakage current,un balance current which relay using for high voltage transmission?

1645


Why field rheostat is kept in minimum position?

721


Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.

1820


sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.

1495


what is cathodic protaction?

1497


What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.

1821


why and how voltage sharing in transformer, during magnetic balance test ?

1812


how many joint can done in HT line and what is life of the joint

1752


How to select a transformer group to connect a 0,433 KV generation with 33 KV grid in bi directional flow of current

1134