Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What are the difference between C-Curve and D-Curve for
MCB's.

Answers were Sorted based on User's Feedback



What are the difference between C-Curve and D-Curve for MCB's...

Answer / s.manivannan

mcb b,c,d,k meaning

Is This Answer Correct ?    1 Yes 4 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / jason

B curve 4x In
c curve 7.5x In
d curve 10x In
c curve is used in most house switchbords. d curve is used where in rush currents are a problem ie motors that do not have soft starting.

Is This Answer Correct ?    5 Yes 9 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / sean foley

answer 11 is pretty much right.
A basic rule of thumb is
B - beyond normal lengths (for very long cables)
C - common (normal) installation
D - Demand on start-up (high initial "rush" current on
motors / heat pumps)

Is This Answer Correct ?    4 Yes 8 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / venkatesh s.r

"C" curve is used only for lighting because of Starting &
runnig current is same in that circuits

"D" curve is used in electronis circuit like
computer.Because of it will be with stand high armonics &
initial rash current.

Is This Answer Correct ?    8 Yes 79 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / g.venkat reddy

MCB are classified as
B,C,D,K curve type

intant..trip current,

C....2-5 times the rated current.(motors,Ltg,inductive
loads)
D....10-20 times the rated current.
(Drives,computers&capacitors)

Is This Answer Correct ?    15 Yes 109 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / bcd

The difference between B, C and is the following.
B is the second letter of alphabet.
C is the 3-th letter of alphabet.
D is the 4-th letter of alphabet.


Thank you for your attention. ... (Take it easy).

Is This Answer Correct ?    39 Yes 178 No

What are the difference between C-Curve and D-Curve for MCB's...

Answer / ismail

C CURVE USED IN INDUSTIAL APPLICATION AND D CURVE USED IN
DOUMASTICK APPLICATION

Is This Answer Correct ?    34 Yes 433 No

Post New Answer

More Electrical Engineering Interview Questions

how many earthing required for ups, what should be the earth voltages

9 Answers   Juniper Networks,


What is the principal of motor?

0 Answers  


What Is HO factor in power selection

0 Answers   Wonderla Holidays,


i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection

0 Answers  


After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.

0 Answers   KSEB, L&T, Siemens,


In 2500kva transformer how much is the withstand High voltage power frequency between primary to secondary and earth? And secondary to primary and earth?

1 Answers   Honeywell,


voltmeter kya hota hy ?

2 Answers  


is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.

0 Answers  


why ct is testing using dc.. y cant we use AC insted of dc on POLARITY TEST.

6 Answers  


why vaccum circuit breakers are preferred over m.o.c.b

2 Answers  


in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.

1 Answers  


what can be the causes of capacitor start motor having a higher current that its actual

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)