Answer / venkat iyer
Selection of CTs depends upon its usage, whether for
metering or protection. Class of accuracy, VA burden and
palatability to instrument safety factors need to be
considered incase of metering CTs. In case of protection
CTs, linearity factor w.r.t its primary current and
accuracy factors need to be considered. Metering CTs are
expressed in terms of Class 1 or Class 3 where as
protection cts are expressed as 5P10 or 5P15 or 5P20 or
10P10 etc. The first digit stands for the class of accuracy
and P stands for protection and the last two digits stands
for linearity.
| Is This Answer Correct ? | 44 Yes | 0 No |
Answer / mervin
A CT used for Instrumentation is required to be accurate
over a normal working range , whereas CT for protection is
required to five a correct CT ratio several times the rated
current . Cores made using Nicel-Iron alloy gives accuracy
upto 5 times the rated current n suitable for
Instrumentation . Cores made using Cold rolled silicon
steel are accurate upto 15 times the rated current and
suitable for protection .An accuracy of about 2-3% is
desirable for distance and differential relays .CT burden
and CT linearity should also be considered during selection
of a CT .
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ramakrishna m
The selection of CT depends on the current ratings of relays
those are used in the protecting circuitry and also depends
on accuracy that circuitry requires.
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / kapil
it depends on the protection circuitary ratings and the
accuracy u desire for the application. it must supply the
rated current to the relays with the accuracy u desire for
ur purpose,and also copper losses in the CTs should be
minimum so it also depends on the laminations and conductor
material u choose.
| Is This Answer Correct ? | 3 Yes | 8 No |
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
what is the diffrence between dol and star delta strater? why star delta starter used instead of dol?
define electrical field?
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current ?
explain how the power is distributed from a power plant to a consumer.explain step wise in detail
Can we provide 3phase wire in conduit for room?
does the Trivector Meter of three phase automatically takes care of the low power factor and gives the reading accordigly or it does not take care of the Power factor while giving the readings please explain
how many types are their in switchyard or substation(like D,I TYPE), what is differant between them
what is pure resistive circuit and pure inductive circuit
How to select cable rating for HT/LT Panels
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
can indirect loading be called as phantom loading?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)