Shall we use Dyn1 transformer in place of Dyn11 for motor application as a distribution transformer
Answer / gururaj kulkarni
Dyn1 will have a phase shift of 30deg on leading side and Dyn11 will have phase shift of 30 deg on lag side. Hence the same can be used. But we can not do parallel operation as there will be dead short circuit
| Is This Answer Correct ? | 7 Yes | 1 No |
What is the voltage violating limit to be considered for load flow study? What is acceptable deviation limit according to relevant standards?
what is mean by unity power factor?why are u calling Resistivity load also unity power factor?
what is the criteria for selection of conductor used for ehv ac electrical dischrge
0 Answers National Productivity Council,
some meggers have three terminals. wat is the real function of the earth terminal?
why transformer calling in VA rating
Explain the Term in CT Name Plate – Class: 5Ps
How the output,losses and temperature of machines varies with linear dimension?
which %age of corona losses increses if frequency is increased to 25%.
3 Answers ADCET, Maihar Cement,
CORRECT INFORMATION ABOUT TRANSFORMERS,what actually transformer is?
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
How we can find the regulation of transformer?
Can I use less voltage cable for neutral, since the voltage of return path is zero ideally?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)