how to select a circuit breaker?
Answers were Sorted based on User's Feedback
Answer / nilesh kumar singh
Selection of Circuit breaker
CURRENT RATING:
Transformer Rating (X)kVA
%age impedance of transformer - Z%
I Full load = X*1000/Sq. root 3*VL
Where X = Transformer rating in kVA
VL = Line Voltage
BREAKING CAPACITY:
Breaking Capacity of the breaker> I Fault Current
Fault Current (Level) = 1.1*VL/Sq. root 3*Z
Where Z = Impedance of Transformer
VL = Line Voltage
Z= %Z*10*(kV)*(kV)/KVA
MAKING CAPACITY:
Making Capacity depends upon the following:
a) Power Factor
b) Instant of switching ratio 'n' between required rate s/c
making capacity and rated s/c breaking capacity.
Is This Answer Correct ? | 66 Yes | 12 No |
Answer / kapil
this depends on the application type where you are using
this circuit breaker. actually we will have to know whether
we require some delay in tripping after the overcurrent or a
frequent operation is needed. if a delay is needed and we
will have to bear some over temperature conditions then we
use thermal relay which has some delay and low trip current
at high temp. when we require the frequent operation then we
use magnetic type relay. also we will have to mind the
operating environment, nominal current rating and max peak
current bearing capacity and delay time of the circuit breaker.
Is This Answer Correct ? | 71 Yes | 25 No |
CB is selected on the basis of it's Breaking capacity,
Making capacity, operating voltage, operating
current,system frequency, insulation level & type of use
i.e indoor or outdoor.
Is This Answer Correct ? | 24 Yes | 8 No |
Answer / mahesh.s
Selection of circuit breaker mainly depends on the voltage
capacity for which its is connected in the circuit like
3.3kv,6.6kv,11kv,33kv,...etc and the breaking capacity of
that breaker means at wht current it will trip the ckt...
and making capacity,
Thermal capacity,
application like indoor or outdoor usage.
Is This Answer Correct ? | 32 Yes | 19 No |
Answer / ammar
we have to calculate the rated current of the load
connected to the circuit breaker from the power equation
p=√3.V.I.cosθ
then we can decide which is the suitable rating for the CB.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / gurbir singh
a ciruit breaker depend upon the total capacity of load
Is This Answer Correct ? | 12 Yes | 6 No |
Answer / magesh
We use circuit breaker for short circuit and overload
protection
For OL -2.5 times of the rated I
For Short circuit-12times of I
According to this calculations breakers are selected
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / andy
people you all are crazy, can you answer simple question
and give simple example ?
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / rk
Rateed voltage
Normal current
breaking curren i.e. fault current fault mva
aux supply volatge
C-O-c seq for auto recl function
Is This Answer Correct ? | 9 Yes | 7 No |
Answer / majid amoudi
direct technical answer:-
suppose if d interviewver asks u
"for 11kva transformer what size of d ckt breaker shud b used"
answer-
11kva= 11,000va
11,000 divided by 220v(depending on various countries voltage rating)=50A
50A is d current passing thru d ckt...according to NEC(national electrical code) current shud be 125%...
so, 50* 1.25=62.5A
d breaker will trip if d current passes more dan 62.5A & d ckt breaker size shud be selected 4 times d nominal ckt breaker current i.e 62.5*4=250A.
so..a MCCB(moulded case circuit breaker) of 250A shud be used for 11kva T/F.
Is This Answer Correct ? | 2 Yes | 1 No |
what is pilot wire protection? wer is it using?
in dc shunt motor if armature wdg is open then
In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)
what are the applications of PLC?
The coils having selfinductancs 10mh and15mh,effective inductance 40mh when connected in series aiding. what will be the equivalent inductance if we connect them in series opposing?
My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor
in 1-phase 230v,how in 3-phase 440v. in each phase in between 230v.
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
What is the RME and explain the full form and what is the RME work?
Name of Hydrocarbon gases.
we have 3*1 MW generator one NGR is common for all it will be selected during paralle our problem is two generator ca be paralled but when slecting third one we need to close NGR selection on third one other wise voltage not matching why?
do we use neutral grounding for resistive balanced load? if we use what happen?