How can we measure and monitor critical performance
parameters of Diesel Generator Sets, both electrical and
engine ?
Answers were Sorted based on User's Feedback
We can measure & monitoring bellows points
A) Engine Related
1) Engine RPM
2) Engine oil Pressure
3) Engine oil temperature
4) Coolant level
5) Coolant temp
6) Governor characteristics
7) Battery charger status
8) Battery charging current & its voltage.
9) Engine running HRS
10) Fuel quantity
11) We can monitor like bellow mentioned alarms
a) Starting failure alarm
b) Charger failure alarm
c) Engine over speed alarm
d) Low engine oil pressure alarm
e) Low coolant level alarm
f) Low DC voltage (Battery Voltage)alarm
B) Alternator related (Electrical)
1) Voltage (line to line & line to neutral)
2) Kw
3) KVA
4) Frequency
5) Amps
6) KW Hrs
7) Pf
We can monitor like bellow mentioned alarms
a) Acb Breaker fail to close alarm
b) Over voltage alarm.
These we can Monitor at computer through software & modbus
converter. Rs 485 0r Rs 232
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / guest
Critical parameters of engine are:
1. Max. torque or breakdown torque
2. max. speed and minimum speed.
3. speed reduction with % of full load.
4.max. working temperature.
5.speed governor charaterestics.
and that of alternator is:
1. starting ampacity
2. max. working insulation/ conductor temperature.
3. frequency variation on % of full loads.
4. voltage drop on % full load.
5. over load capacity
Is This Answer Correct ? | 2 Yes | 2 No |
what is integrated ac contact circuit
which one is the most common system for secondary ditibution
Dear all, kindly give me the details of leectrical design engineer course details/institute in hyderabad /any where in india.
Is there any problem ,if R-Y-B voltage is constant , but the air compressor taking one phase high current.what is possible causes.the said compressor is very new.(55kw).
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,
75 kw motor take 45 amp in no load delta in star 10 amp but in load it will take 160 amp but IR velue of winding above 500 at 1kw ph to earth and ph to ph. what problem it should be?
How to Design green buildings services? What is the advantage to design green building?
How to calculate cable sizing
why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our system?
10 Answers ABB, Georgio Rocks, Piramal Healthcare, Zenith Engineering Corporation,
why the current leads voltage in the case of a capasitor
what is metering cum synchronizing panel and how it is used?
What is the difference between Floot charge and Trickle Charge.