difference between over current and over load protection?
Answers were Sorted based on User's Feedback
Answer / raji
IN AN ELECTRICAL CIRCUIT IF THE CURRENT EXCEEDS THE
SPECIFIED LEVEL(FULL LOAD CURRENT) IS CALLED OVER CURRENT.
TO PROTECT THE MOTOR OR ANY ELECTRICAL EQUIPMENT FROM OVER
LOAD(OVER LOAD CAUSES WINDINGS MAY BURN OUT OPEN ETC.,)SOME
CIRCUITS ARE PROVIDED TO PROTECT THE MOTOR THIS IS CALLED
OVER LOAD PROTECTION..eg., IN DOL STARTER OLR IS PROTECT
THE MOTOR FROM THE OVER LOAD
Is This Answer Correct ? | 10 Yes | 7 No |
Answer / harry
Overcurrent protection is protection against excessive
currents or current beyond the acceptable current rating of
equipment. It generally operates instantly. Short circuit is
a type of overcurrent. Magnetic circuit breakers, fuses and
overcurrent relays are commonly used to provide overcurrent
protection.
Overload protection is a protection against a running
overcurrent that would cause overheating of the protected
equipment. Hence, an overload is also type of overcurrent.
Overload protection typically operates on an inverse time
curve where the tripping time becomes less as the current
increases. Overload relays as well as “slow blow” fuses are
commonly used to provide overload protection.
Some devices provide both overcurrent and overload
protection. A thermal-magnetic circuit breaker has both
thermal (overload) and magnetic (overcurrent) elements. Both
elements operate as described above. Likewise the dual
element fuse has both instantaneous and inverse time
characteristics in the same fuse providing both overcurrent
and overload protection.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / manas
Over current:
The full load current capacity, if it exceeds the rated full
load current it is over current.
Over Load Protection:
Protection given to the electrical equipment to safeguard it
from buring during the fault level or overloading.By
performing tripping action.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / harry
Overcurrent protection is protection against excessive
currents or current beyond the acceptable current rating of
equipment. It generally operates instantly. Short circuit is
a type of overcurrent. Magnetic circuit breakers, fuses and
overcurrent relays are commonly used to provide overcurrent
protection.
Overload protection is a protection against a running
overcurrent that would cause overheating of the protected
equipment. Hence, an overload is also type of overcurrent.
Overload protection typically operates on an inverse time
curve where the tripping time becomes less as the current
increases. Overload relays as well as “slow blow” fuses are
commonly used to provide overload protection.
Some devices provide both overcurrent and overload
protection. A thermal-magnetic circuit breaker has both
thermal (overload) and magnetic (overcurrent) elements. Both
elements operate as described above. Likewise the dual
element fuse has both instantaneous and inverse time
characteristics in the same fuse providing both overcurrent
and overload protection.
Is This Answer Correct ? | 1 Yes | 4 No |
What it indicates by 25/41MVA on transformer?
how will be the capacitance generated in a earthed wire???
What are the classifications of heating element?
HOW SKIN EFFECT REDUCE THE CROSS SECTION OF THE CONDUCTOR
what is the relative size of single and three phase?
what is the significant for using two types of voltage(line voltage & phase voltage)
what is the reason for using 110 volt and 60 hertz ac supply for using power distribution in America?
I have CNC Turning lathe,while doing electrical preventive maintenance what should I do & please brief me plan & shedule for the same.
what is phase to phase fault? what is line to line fault?
whye the current increases in the motor when the load on the motor increases
WHY THE +VE POLARITY OF 48V DC POWER SUPPLY IS USUALLY GROUNDED?
I WOULD LIKE NOW WHY WE CANT USE SOME CT FOR MESARING AND PROTECTION