I decided to provide a 11KV / 440V Xformer in my Substaion.
What are the protection required for that?
Answers were Sorted based on User's Feedback
Answer / ajay
for H.V side u can use R.M.U whc include SF6 C.B and For LT
side ACB
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / nirajan poudel
11000/440v means it is step-down transformer.so, for MV
side use 9kv LA,11 kvDO-FUSE and switch gear panel which
includes VCB which is used for isolating the transformer
during maintenance period.For LV side use TP MCCB for 3-
phase bus bar(R,Y,B) and use SP MCCB for 1-phase bus
bar.And there must be provision for AMF (Automatic Main
Failure Panel) to change the supply from main line to stand-
by generator and vice-versa with respective CB tripped.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ajay pal
transformer are to be fully earthed ,neutral grounding
resistor are to be provided, transformer overhead
differential protection , transformer oil for cooling is
very necessary ,
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / doli tomar
11000/440v means it is step-down transformer.so, for MV
side use 9kv LA,11 kvDO-FUSE and switch gear panel which
includes VCB which is used for isolating the transformer
during maintenance period.For LV side use 4P ACB /MCCB for
3-
phase bus bar(R,Y,B) and use overcurrent, overvoltage,
undervoltage,IDMT,Single phase preventer,restricted earth
fault relay because Relays are used where it is necessary
to control a circuit by a low-power signal (with complete
electrical isolation between control and controlled
circuits), or where several circuits must be controlled by
one signal.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rakesh
Transformer Secondary star neutral need to be earthed.
Separate earthing pit need to be provided.
| Is This Answer Correct ? | 3 Yes | 6 No |
how we can check new PT ? without name plate.
1 Answers Indo Power Projects,
Write the force balance equation of ideal dashpot element.
calculation of lad carryinc capacity of 6mm2 cross section wire in 415 voltage circuit. What will be the amps.
HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER FEEDER AT START AND RUNNING?
How to improve fuel cell in a distribution system?
what is the unit of current
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
why neutral is neccessary?
Should power factor be low or high?
why current transformer secondary side should be shorted ?
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
Two 11 kv lines are feeding to common bus in a substation,I have one set of CT & PT(3ct,2pt), How can I measure both lines power using single set.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)