why we generally use 3.5 core cable or in other word 1/2
core for neutral and also confirm me that in balance
conditiob(3 phase)current in neutral will zero
Answers were Sorted based on User's Feedback
Answer / dkmathur
In a three phase circuit theoritically there will be Zero
current in Neutral. But due to un-balancing of phases
practically phase voltage becomes unequal with the result
some current flows in neutral.That is why neutral is of
half rating only.
Is This Answer Correct ? | 66 Yes | 12 No |
Answer / pardeepkumar
Neutral conductor must be 1/2 the size of other
conductor.It is theoraticaly expalin that algebric sum of
all the phases when in balannce condition then neutral
current will be zero.
Now suppose one phase fail i.e total unbalace condition its
neutral conductor will provide a return path and its
current will be half the load on other phases.so by this
result on neutral conductor for every unbalance condition
its current will not exceed the rated than other phases.
Pardeep.kumar
Engineering Dept.
Panacea Biotec Ltd.
Is This Answer Correct ? | 24 Yes | 8 No |
Answer / raju chetiar
Normally Neutral conductor is 1/2 the size of other
conductor.It is theoraticaly expalin that In a three phase
circuit ( Equal load in all three phasse) there will be
Zero current in Neutral, Ex. 3phase indusction load (Motor)
(NO NEUTRAL CONNECTED T OANY MOTORS AS THE RESISTANCE OF
THE THREE WINDINGS ARE EQAL).
But in a three phase to single phase distribution
(Resistive loads) it is not possible to maintain the equal
load in all three phases hence the unbalance current has to
be taken away from the circuit for the healthy opertion of
the equipmetns.
Thearitically and also practically it is prooved that the
flow of unbalance current in the 3 phase resistive load
distribution is always less than 1/2 of the phase current.
So 1/2 caore has been taken as a neutral
Is This Answer Correct ? | 10 Yes | 5 No |
Answer / john hancock
The choice of whether to use a neutral of equal size to the
phase conductors depends on your design criteria and load
equipment. The difference of the load being delta, floating
star or star with a neutral point
A 3 phase circuit in balance will produce little or no
neutral current contribution.
However a 3 phase circuit imbalance will produce neutral
currents as per the following formula
A^2 + B^2 + C^2 - AB - AC - BC).
A three phase circuit wired in star with the neutral at the
star point will operate with null balance if the loads are
equal, it is possible (and I have seen this) for 2 phases
to fail and leave one phase connected to the load and
neutral. The neutral current becomes equal to the phase
current, the designer of the circuit failed to account for
this, the undersized 1/2 neutral overheated and caught fire
destroying the switchgear and damaging the furnace.
I would urge anybody to carfully consider all possible
outcomes when choosing neutral cable sizes as flames coming
out of a switchboard often alarms the unwary.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / sangekar vaijnath
Generally it depend on load, If cable is used for inductive
load e.g.motor, if there is any fault then 1/2 core is
sufficient to carry fault current due to lagging power
factor. However, in resistive load we are using 4 core
cable since there is no power factor.
Is This Answer Correct ? | 9 Yes | 21 No |
Answer / mritunjay singh yadav
for using 3-phase supply in any instrument neutral is also
required since neutral capacity is just half to the phases.
we dont need to use 4 core thats cost matter..
Is This Answer Correct ? | 0 Yes | 24 No |
Answer / blake australia
Any switch mode power supply (computer, UPS, AC/DC
transformer) has some leakage current and imbalance. In
data centres they are starting to use full size neutral
cables to account for this. Basically only need 1/2 size in
motors, saves money on expensive copper
Is This Answer Correct ? | 5 Yes | 36 No |
what are the main components of fan?
I have made a 3 phase thyristor full bridge rectifier. But at the moment it is working only for the half bridge operation. Both the half bridges are on operation separately but when i put it into full bridge operation the oscilloscope output is zero. I rechecked that the pulses are correct for each thyristor. what could be the possible reason for this?
i need circuit star delta connection?
why swityard is necessrry requirement in any bis power distributin systems?
what is the difference between the voltage of 5 volts capacitor and and 5volts battery?
which of the following is the earliest known literary source of ancient india and indeed of mankind
What is LT? And specify the range of voltage?
why AC voltage source are generate as 50 Hz ?
how flow current in 220 kv line to line
In secondary transmission i.e., in distribution side, supply for homes are connected through different phases in order to balance the 3 phase load. But in practical we saw nearby house doesn't have power due to single phasing. But other two phases give supply. How it's possible? it doesn't make "single phasing"?
plz send me the placement interview question and answers of whizchip(technical and apttitude)..i have an interview in next.
How to Convert horsepower to kva? what is the three phase formula? email me if u know thanks Rehan smileavail@msn.com