Explain role of Buckolz Relay in Transformer ?
Answers were Sorted based on User's Feedback
Answer / niloy
Buckolz Relay is connected between transformer tank and
conservator.It gives protection from mainly over
heating.The overheating can be done by any way-- by
sparking or by short circuit or by any internal fault.When
transformer oil overheated it decomposes itself and create
some hydrocarbon and produce hydrogen gas.. This light
weight hydrogen gas moves to the upward direction and trap
into the buckolz relay.After collecting a sufficient
ammount of gas the buckolz relay give a alarm signal and
trip the breaker to protect the transformer to getting
damaged from over heating.
We can collect the gas stored in the buckolz relay and can
analyse it to know the types of fault.In big transformer a
gas holder is connected to the buckolz relay to collect the
gas..
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / tango
Buchholz Relay is a gas actuated relay installed in the oil
immersed transformer for the protection against all kind of
faults. It is used to give an alarm in case of slow
developing faults in the transformer and to disconnect the
transformer from the supply in the event of severe internal
faults, always used for transformer having rating exceeding
75 kVA.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pillay
I wish to add to TANGOS answer.When faults due to insulation breakdown,sparks within the windings or due to insulating oils
properties breakdown which may cause the developments of air within the transformer.This air bubble is used to activate the
BUCKHOLZ relay and trip off the transformer.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / anil
Buchholz Relay is a gas actuated relay. The main advantage of this relay when compared to other type is, it will give alaram
Before,in the case of internal fault. That means a operator can take the preventive means and he can operate,other wise it will trip automatically.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
Thanks mr sharma.It should had been gas instead of air in my answer but I didnt know it was hydrogen gas.Thanks again.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravinder sharma
sorry pillay sir this is not air ,this is hydrogen gas .
| Is This Answer Correct ? | 2 Yes | 2 No |
what is the reactive power what is the use of it in system
What is the problem, if a circuit breaker is not closing.
What is the use of starter in tube light fitting.how it works.
What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.
What are the main problems in distribution? I have to do an assignment so which problem should I choose? Like power factor problem etc.
Dg daily a check duration
List the disadvantages of constant k filters?
1 KW = how many kva
from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?
why not feeling shock while touching rotor shaft of induction motor during running condition? during running condition emf induced in rotor.
what's the difference between induction generator and synchronous generator?
How power factor of electric system improved?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)