11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / manir hussen
for above mention requirement we can use 2 nos. of CT & 1
PT
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / malik waseem
what is difference between metering CT and protection CT
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / mayil
primary o/c & E/F -1 CT
SEC o/c & E/f - 1 ct
stand by e/f - 1 ct
pry & sec metering - 2 ct
primary pt - 1 pt
| Is This Answer Correct ? | 2 Yes | 9 No |
what happen if rotor earth fault in AVR system?
what is total power generation in tamilnadu What are the methods used powerfactor improved? which place DC transmission line usde?
DIFFERENCE B/W NEUTRAL AND EARTH?
Why DG self motor winding burnt out?
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
What is the function of Harmonics filter, and how to calculate that rating of the energy saving?
why ahould you show client/engineer activities clearly on the project plan
what will be the breaking capacity of MCCB of 1000kVA (6% Impedence) transformer? Voltage being 415V, Power Factor 0.8.
what is the difference between the voltage of 5 volts capacitor and and 5volts battery?
what is the difference SCR & TRIAC?
how mach PF mainten in DG
Define what is power quality meter ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)